Your interpretation is basically that only electrodes that don't meet the requirements for NEC electrodes (e.g. an unlisted 6ft rod) can be used as auxiliary electrodes. That's an interpretation I've never heard before and I think would strike many as absurd. Go back and watch Mike Holt video I posted earlier where he explains that 250.54 was put in the code to head off conflict between the code and manufacturer instructions that require a grounding electrode for equipment. If the manufacturer instructions require an electrode that meets NEC requirements (or if some dirt worshipping engineer puts one in a job spec for a subpanel), then my understanding is that 250.54 is intended to apply regardless of the characteristics of the electrode.
I'll stick with I can attach any electrode to an EGC by itself because 250.54 plainly says so. That's the whole point of that section. 250.54 explicitly exempts from 250.50 in a way that 250.50 does not explicitly include the electrodes in 250.54.
It's also worth taking a look at 250.60, which is another example of electrodes that aren't considered to be covered by 250.50.
That’s not my interpretation at all . 250.50 specifically says all grounding electrodes described in 250.52(a)(1-7) that are present at a structure shall be bonded together forming the GES for the building . (A(1-3) is metal underground water pipe , metal in ground support structures, and CEE, ) then says if none of those electrodes exist one or more of the grounding electrodes specified in A(4-8) shall be installed and used. A(4-8) are Ground ring , rod and pipe electrodes , other listed electrodes, and plate electrodes, and other metal underground systems . We cant install A(1-3) so if any one of those 3 are present they they must be part of the GES, 1-3 have to be part of the GES and only the GES if they are present, uou can not use a metal underground water pipe electrode as a auxiliary electrode because we cant install it and if its present it must be part of the GES same thing does for a CEE and the metal in ground support structures . Any one of the grounding electrodes specified in 250.52(A)(4-8) could be used as either the GES or auxiliary electrode or both . You can have a metal underground water pipe electrode , supplemented by rod type electrode to make up your GES and your gec and or bonding jumpers connect to the grounded service conductor, then you can have a non separately derived system generator and can use another ground rod as a auxiliary grounding electrode that connects to the equipment . But does not tie into the GES . My whole point has been and maybe I’ve worded it incorrectly . If any of the electrodes describe by 250.52(A)(1-3) are present at at building those 3 specific grounding electrodes must be part of the buildings GES when available . You can any of those as auxiliary grounding electrodes because we cant install install any of those 3 types of electrodes . Any of the electrodes specified by 250.52(A)4-8 could be part of the GES and/or used as a auxiliary grounding electrode but say you have a set of ground rods as part of your GES then a seperate ground rod for an auxiliary electrode the connections must remain seperate . Hopefully that’s a better explainstion .
Sent from my iPhone using Tapatalk