Definitely fuses. You can use a larger breaker ahead of the fuses if you wish or need to.Here is the name plate
Seems odd to me to reject a perfectly legal installation.I will always enforce what is on the actual equipment over what is in the instructions. With that nameplate I am going to require a fuse as the overcurrent protection.
Read the installation manual.The literature I found definitely says fuse. I don't see breaker.
The equipment manufacturer is in the unique position to decide what is best for their equipment.Oh, poor you.
When I asked what difference it would make (CB or fuses), LarryFine replied "Because it's also about protecting the compressor unit."
The equipment manufacturer says you can use fuse or breaker.The equipment manufacturer is in the unique position to decide what is best for their equipment.
It has to do with the UL testing procedures. Probably the manufacturer cheaped out and only paid for the fuse testing.OK, but what's the difference between fuses and a CB for this purpose? Is it that a CB might respond more quickly and trip during startup where fuses would not blow? I am not an HVAC expert.
I agree with those who select to follow the specific equipment's attached nameplate over the more general included printed instruction sheet.Read the installation manual.
Doesn't the manufacturer also choose what to print on the nameplate?The equipment manufacturer says you can use fuse or breaker.
I thought the manufacturer decides what's best for their equipment.I agree with those who select to follow the specific equipment's attached nameplate over the more general included printed instruction sheet.
Yes. Nothing on the nameplate says that you can only use fuses.Doesn't the manufacturer also choose what to print on the nameplate?
The fact that it says fuse limits you.Yes. Nothing on the nameplate says that you can only use fuses.
No it doesn't. The manufacturer tells you that you can use a breaker.The fact that it says fuse limits you.
Or they just don't understand how the rules work.With that nameplate I would make the same call as the inspector (fuse required).
My understanding is that units so marked have only been evaluated (listed) using the fuse as protection.
The unit has not been tested to assure a C/B will provide adequate protection.
(It may boil don to the manufacturer not wanting to pay for testing/listing with a C/B)
In addition, failure to use a fuse might well void any warranty
UL does not agree that it would be a legal installation. The product standard covers the require markings on the nameplate. The UL Marking and Application Guide for Electrical Heating and Cooling Equipment makes it clear that where the manufacture chooses only to say "fuse" on the nameplate, that is the only type of OCPD that permitted to be used. If they want to permit the use of a circuit breaker, they must put that marking on the nameplate. Putting it only in the instructions does not comply with the requirements of the product standard.Seems odd to me to reject a perfectly legal installation.
Caveat to the following: I've only browsed maybe a dozen UL standards, and generally just skim them as they are so long. So I'm not as familiar with them as I am with the NEC.UL says that you can only use fuses.
44.3(i) For each hazardous voltage circuit which powers more than one motor or a motor and other loads rated 1.0A or more as shown in Figure 44.2 (see Clause 44.15) "MAX. FUSE _____" or "MAX CKT. BKR. _____" or "Maximum overcurrent protective device."
44.3(x) Where required by Clause 76.1, the following marking or equivalent, "CAUTION: USE TIME DELAY FUSES."
It does say that ( https://code-authorities.ul.com/wp-content/uploads/2014/04/EHCMG_AG.pdf ), in particular (Section 17 in part):The UL Marking and Application Guide for Electrical Heating and Cooling Equipment makes it clear that where the manufacture chooses only to say "fuse" on the nameplate, that is the only type of OCPD that permitted to be used.
The markings for short-circuit and ground-fault protection always include some indication of the type of protection device as well as the maximum current rating. This is significant since the various types of devices recognized by the NEC® to provide this protection do not necessarily provide the same level of protection for all units. Briefly, if the marking indicates:
1) Only “Fuse,” then only fuses are to be used;
2) “Circuit Breaker” and “Fuse,” then either fuses or circuit breakers
3) “Fuse or Circuit Breaker” or “Overcurrent Protection,” then fuses or any type of circuit breaker (including “HACR Type”) may be used.