When I started doing electrical inspections in 1990 I was at a mobile home park it was raining and I touched the metal siding of a mobile home and received a shock.
Later discussing the incident with the electrical inspector who was involved with the hiring of me, he said you could get shocked from touching a mobile home with the meter pulled, I looked a little confused and he said that’s one of the reasons they require an insulated equipment ground for the direct buried cable that supplies the mobile home.
Never forgot what he said, took me awhile to begin to understand why he said it.
I'm not sure I see how, I do see how you are reading it that way, I think it would need a comma for that to be trueOne could interpret this as it either has to be insulated, whether aluminum or copper.
or
just covered copper.
JAP>
I considered that reason... and it truly does not hold up in most cases. Could be it's in the Code because others think of it same as you. The only time it holds up is when an isolated ground is justified. We see how that concept of IG receptacles has been relegated practically to dust, but there are still a few justifiable cases.
the text says insulated or covered copper.
it seems to be indicting copper UF cable as one of the approved methods it does not read to include insulated Alum.
if bare copper is buried in contact with soil could it pick up current and elevate the current on the equipment ground
It could if there is a large voltage gradient in the earth, such as from a faulty POCO MGN.if bare copper is buried in contact with soil could it pick up current and elevate the current on the equipment ground
But that doesnt tell you covered with what.
With reading it that way I could interpret it as covering a bare copper wire with dirt.
JAP>
Conductor, Covered. A conductor encased within material of composition or thickness that is not recognized by this Code as electrical insulation.
Any voltage gradient would cause current to flow. Doesn't have to be large at all.It could if there is a large voltage gradient in the earth, such as from a faulty POCO MGN.
JAP>
Jab you usually have insightful comments is there a point you are trying to make about covering the conductor with dirt?
No.
Just still trying to figure out what your point is.
JAP>
No.
JAP>
My guess is first it's not that it's indoors but more that it is not underground (i.e. in direct contact with earth)....
In other applications such as swimming pools, and If part of the goal was to prevent the equipment ground conductor contacting other conductors that may be a fault clearing path or a grounded circuit current path, why remove the insulation requirement when the conductor was indoors verses outdoors?
I think this particular one is a matter of conformity with HUD regulations. Compliance with HUD is automatic because its regulations are a matter of federal law. The NEC at best is adopted at the state level.M...
The NEC in article 550 is specific enough to say the feeder equipment ground is not to be re-identified by baring the conductor, as an added measure to make it clear the equipment ground is to maintain its insulation even on the small portion that is being trimmed out and landed in the panel.
My point in part on a manufactured home installation for instants. An installer has a permanent foundation double wide setting on a block foundation. The service disconnect is on the structure mounted to the siding. The contractor runs SER cable to the manufactures homes distribution panel 75 ft under the homes in a crawl space.
At the inspection the installer / contractor is told he wasn’t allowed to use SER why because the code says insulated equipment grounding. The manufactures instruction say a feeder with a green insulated equipment ground.
I’m not obligated to justify what the code says but it would be helpful when this correction is going to cost the installer hundreds of dollars to change I have a clearer understanding than the code says so.
This is applicable to when a installer runs copper UF cable to a pool pump, and they say the conductors insulated and I even ran it in conduit as an extra measure.