When someone runs a post hole digger through their pivot or well underground we butt splice and heat shrink the conductors and use a conduit splice kit to repair the conduit, never to be seen again.
Your situation, we would repair conduit and pull new wire.
Same here also. Inside a building I would not settle for anything other than new wire.Same here.
Out on the farm is different. I'm not going to tell the old farmer he needs fifteen hundred feet of new wire. I'm just glad that they call us instead of using romex connectors and duct tape for the repair. Oh, wait, I saw that once.