What do you gentlemen think of this email?
Good afternoon this is the second time I've had an inspector fail me for this installation and i'm looking for some clarification. The inspector stated I am violating 240.21. Clearly this is not a tap as per the NEC definitions is A conductor, other than a service conductor, that has. overcurrent protection ahead of its point of supply that exceeds. the value permitted for similar conductors that are protected as. described elsewhere in 240.4
my argument is article 230. 90 (A)(1) Exp 3, specifically states Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
the above exception depicts and clarifies the installation I have below please see attached photos. The conductors in the picture that land directly on the bus in the service switch that is rated for use as service equipment are directly coming from the utility size number 2 copper conductors
Sent from my SM-G986U using Tapatalk