Isn't that what post #64 says, the Ex rules only apply to ocpd's 2/3/4/5/6, and not to just one ocpd?
No, that not what post #64 says.
Why would the rules of Ex3 not apply to a single ocpd?
Because a single (1) ocpd is not "two to six circuit breakers or sets of fuses"
I assumed the "sum" rules and "calc load" rules applied to ALL devices used as ocpd's that serve as the disco/ocpd for SEC's.
They do. Your example calculated a load of 310A and gave a service conductor ampacity of 185A. The calculated load exceeds the ampacity of the service conductors, so your example does not comply with 230.90(A) ex 3.
one set 3wire 240vCT SEC » service box » 6 ocpd's
Ampacity of SEC's = 185A
ocpd 1 = rated 200A
ocpd 2 = rated 40A
ocpd 3 = rated 40A
ocpd 4 = rated 40A
ocpd 5 = rated 40A
ocpd 6 = rated 40A Sum of ratings of ocpds = 400A
Calc load for ocpd 1 = 160A
Calc load for ocpd 2 = 30A
Calc load for ocpd 3 = 30A
Calc load for ocpd 4 = 30A
Calc load for ocpd 5 = 30A
Calc load for ocpd 6 = 30A Calculated load = 310A
If your SEC ampacity was 335A, rather than 185A, the installation would be compliant.