Lobster tank GFCI protection?

Status
Not open for further replies.
Not now, I will start a thread later. We can use this post as a basis if you want, but you are gonna have to lead me through in baby steps.

Trying to explain to me in the middle of this thread is a bad idea IMO. It will get muddled.

gotcha
just wetting your appetite
 
gotcha
just wetting your appetite

Yes, thank you. I am interested.

I also was making a point to buggy-mbrooke-that it is a simple matter to seek information and discuss a subject with someone versed in the matter without being a sycophant/toady.

If I question something you say, you can show me the math and why you came to that opinion/conclusion and discuss the differences. Simple discussion.

I get a free education if I play my cards right and simply say what I know, what I do not know, and go back and explain that again-I am confused.

It really is not that hard, but he will not listen. Sigh.
 
I don't think that's true. I would think that the resistivity of rainwater would be higher than that of tap water. I have an outdoor receptacle on a GFI circuit; every time it rains and I have left the cover open on one of the outlets, the GFI trips.
I believe that the problem in your case is similar to leakage on high voltage lines at the first rain: it is not the resistivity of the rainwater that causes the leakage, it is the resistivity of the dry surface layer of dust and chemical crud when it is moistened by the rainwater.
Alternatively you can think of it as the water with surface crud dissolved in it.
If your GFCI receptacles were clean, rainwater should not cause a trip.

Sent from my XT1585 using Tapatalk
 
The tank does not require GFCI per 210.8(B). No other section supercedes this.

Additional protection via GFCI is a design choice.

I chose to add it.

Good choice. I would as well.

It's interesting that the OP's scenario sort of dances around several common GFCI requirements without falling under any. One would think that any equipment that has a portion of it submerged or otherwise in direct contact with a decent quantity of water would be required to have GFCI protection. There certainly are less dangerous areas that do require it....like kitchen countertops beyond 6 ft. from a sink...
 
Good choice. I would as well.

It's interesting that the OP's scenario sort of dances around several common GFCI requirements without falling under any. One would think that any equipment that has a portion of it submerged or otherwise in direct contact with a decent quantity of water would be required to have GFCI protection. There certainly are less dangerous areas that do require it....like kitchen countertops beyond 6 ft. from a sink...

Yes, the OP scenario does not really directly fit into a category.

Erring on the side of caution here seems prudent given the small cost.
 
Thread exploded since I last read it.

Pool bonding isn't done for the sake of GFCI's as much as it is done for equipotential reasons.

And why doesn't a 3 phase hard wired pool motor require a GFCI?

I am going to say that you don't know the full reasoning behind GFCIs. Its not water alone, but rather that water, dirt, and concrete lowers the impedance of the human body substantially. A missing EGC in those scenarios could actually be lethal. As could direct contact.
Three phase GFCI for pool pump- I bet is coming sometime. Does it need to? IDK. I think the risk is pretty low most installations.

I agree water alone isn't supposed to be driving force for GFCI protection. It is a factor for increased conductivity of many items though, which is a driving force.

coincidence
the population increased by 35% in the timeframe 1976-2000
Meaningless without more data on births and deaths, and even immigration.


After 17 pages, I didn't see any code article mentioned that might be interpreted as being a requirement, which is what the OP asked. I readily admit to getting bored with the bickering by page 4, and only picking as far back as page 15, so if anyone actually mentioned a relevant code article, I could have missed it.
Correct, no direct requirement for GFCI just because we have a fish tank. Other aspects may trigger GFCI requirements, and is not NEC violation to put them in for design reasons.
Some instances may be pretty good design reason, others the risk just isn't much different than it is for other utilization equipment.

Does one need to use GFCI protection if they plug in a hot plate and then put a pot of water on it? If it is on a kitchen countertop the protection is already required as a general rule, but say I plug in temporarily in my office or somewhere that isn't generally GFCI protected? We also boil water on electric cooktops or ranges but don't GFCI protect them as a general rule, though that is in the process of changing in 2017 NEC (and seems may expand in future codes) as a cord and plug protected appliance in a commercial kitchen likley will require GFCI, but still does not apply to hardwired appliance - I would think potentially missing EGC on cords is somewhat of a factor here, without that the risk is same either way IMO.

I don't think that's true. I would think that the resistivity of rainwater would be higher than that of tap water. I have an outdoor receptacle on a GFI circuit; every time it rains and I have left the cover open on one of the outlets, the GFI trips.
Tap water varies everywhere you go. Rainwater does as well, at least right when it first when it starts raining.

Pure water is a poor conductor, but water easily dissolves a lot of things that will make it more conductive.
 
.

I also was making a point to buggy-mbrooke-that it is a simple matter to seek information and discuss a subject with someone versed in the matter without being a sycophant/toady.

If I question something you say, you can show me the math and why you came to that opinion/conclusion and discuss the differences. Simple discussion.

I get a free education if I play my cards right and simply say what I know, what I do not know, and go back and explain that again-I am confused.

It really is not that hard, but he will not listen. Sigh.



Just because you see numbers does not mean the argument is correct or logical. Yes Ingenuirs math is correct, but in this case the wrong numbers are being used and the wrong assumptions being made. Here is one example:


http://forums.mikeholt.com/showthread.php?t=192766&page=9&p=1932314#post1932314

Yes Ingenuir would be correct if the loop impedance was 60ohms, how ever come real world the odds of you finding 60ohms EFLI on a 120 volt outlet wired to code are near zero. Even the doc I linked says the absolute minimum under worse case conservative estimates was 75amp.
 
I believe that the problem in your case is similar to leakage on high voltage lines at the first rain: it is not the resistivity of the rainwater that causes the leakage, it is the resistivity of the dry surface layer of dust and chemical crud when it is moistened by the rainwater.
Alternatively you can think of it as the water with surface crud dissolved in it.
If your GFCI receptacles were clean, rainwater should not cause a trip.

Sent from my XT1585 using Tapatalk

Thanks. I'l go out there and hose down the open receptacles to solve the problem. :D
 
Good choice. I would as well.

It's interesting that the OP's scenario sort of dances around several common GFCI requirements without falling under any. One would think that any equipment that has a portion of it submerged or otherwise in direct contact with a decent quantity of water would be required to have GFCI protection....
Like a submersible well pump?
 
Correct, no direct requirement for GFCI just because we have a fish tank. Other aspects may trigger GFCI requirements, and is not NEC violation to put them in for design reasons.
Some instances may be pretty good design reason, others the risk just isn't much different than it is for other utilization equipment.

Does one need to use GFCI protection if they plug in a hot plate and then put a pot of water on it? If it is on a kitchen countertop the protection is already required as a general rule, but say I plug in temporarily in my office or somewhere that isn't generally GFCI protected? We also boil water on electric cooktops or ranges but don't GFCI protect them as a general rule, though that is in the process of changing in 2017 NEC (and seems may expand in future codes) as a cord and plug protected appliance in a commercial kitchen likley will require GFCI, but still does not apply to hardwired appliance - I would think potentially missing EGC on cords is somewhat of a factor here, without that the risk is same either way IMO.

Indeed, why did dishwashers get a GFCI requirement and not ranges? Or for that matter, refrigerators with cold water and ice delivery? All three appliances either have water on or in them and can potentially have a scenario of a person in wet contact with the appliance. All three are very often well within 6 feet of a sink.
 
I am serious.
I'm sure the CMP were too. There's no way a GFCI would prevent the overheating control panel fires plaguing Whirlpool and associated brand dishwashers....the culprit circuitry does not fault to ground. The Bosch, etc. models that have overheating power cords? Maybe.
 
I'm sure the CMP were too. There's no way a GFCI would prevent the overheating control panel fires plaguing Whirlpool and associated brand dishwashers....the culprit circuitry does not fault to ground. The Bosch, etc. models that have overheating power cords? Maybe.

I meant I was serious about the rumor or such. Did not say it was gospel or that I agreed.

I do not wire DWs so I ain’t really interested in the back story or substantiation for the code, I just was sayng I am pretty sure there was back room politics/shenanigans involved. Don G I think may have brought it up. Do not remember.
 