Thread exploded since I last read it.
Pool bonding isn't done for the sake of GFCI's as much as it is done for equipotential reasons.
And why doesn't a 3 phase hard wired pool motor require a GFCI?
I am going to say that you don't know the full reasoning behind GFCIs. Its not water alone, but rather that water, dirt, and concrete lowers the impedance of the human body substantially. A missing EGC in those scenarios could actually be lethal. As could direct contact.
Three phase GFCI for pool pump- I bet is coming sometime. Does it need to? IDK. I think the risk is pretty low most installations.
I agree water alone isn't supposed to be driving force for GFCI protection. It is a factor for increased conductivity of many items though, which is a driving force.
coincidence
the population increased by 35% in the timeframe 1976-2000
Meaningless without more data on births and deaths, and even immigration.
After 17 pages, I didn't see any code article mentioned that might be interpreted as being a requirement, which is what the OP asked. I readily admit to getting bored with the bickering by page 4, and only picking as far back as page 15, so if anyone actually mentioned a relevant code article, I could have missed it.
Correct, no direct requirement for GFCI just because we have a fish tank. Other aspects may trigger GFCI requirements, and is not NEC violation to put them in for design reasons.
Some instances may be pretty good design reason, others the risk just isn't much different than it is for other utilization equipment.
Does one need to use GFCI protection if they plug in a hot plate and then put a pot of water on it? If it is on a kitchen countertop the protection is already required as a general rule, but say I plug in temporarily in my office or somewhere that isn't generally GFCI protected? We also boil water on electric cooktops or ranges but don't GFCI protect them as a general rule, though that is in the process of changing in 2017 NEC (and seems may expand in future codes) as a cord and plug protected appliance in a commercial kitchen likley will require GFCI, but still does not apply to hardwired appliance - I would think potentially missing EGC on cords is somewhat of a factor here, without that the risk is same either way IMO.
I don't think that's true. I would think that the resistivity of rainwater would be higher than that of tap water. I have an outdoor receptacle on a GFI circuit; every time it rains and I have left the cover open on one of the outlets, the GFI trips.
Tap water varies everywhere you go. Rainwater does as well, at least right when it first when it starts raining.
Pure water is a poor conductor, but water easily dissolves a lot of things that will make it more conductive.