Lobster tank GFCI protection?

Status
Not open for further replies.
ohm m
pool L = 10, coss section 10 x 2 = 20

pool
R = 0.4 x 10/20 = 0.2 ohm

drinking
20 to 2000
thin puddle
L = 1 mm = 0.001 m
A = 1/4 x 1/4 = 1/2 sq m
R = 20 x 0.001/0.5 = 0.04 Ohm
R = 2000 x 0.001/0.5 = 4 Ohm

all <<<< body Z
you know not of what you speak


Swimming pool water[j]3.33×10−1to 4.00×10−10.25 to 0.30[32]
Drinking water[k]2.00×101to 2.00×1035.00×10−4to

Real number and real concepts, again taken out of context in relation to the discussion at hand.

You are claiming water will trip an OCPD, even a GFCI all the time- but as your numbers show water and electrode surface area and distance play a role.
 
it is not I who lack understanding :lol:

all 20 code sections relate to water/moisture

And concrete among others- why does an unfinished basement need GFCI but not a finished one?

All these areas are places where conditions lower body contact resistance and/or (body) fault path be it concrete, dirt, moisture, grounded object likely to be in reach, ect. In this cases an energized object is very likely to be lethal.



BTW, differential technology existed before Dalziel. Technically he did not invent the device that trips on such a scheme:



The first residual current connection circuit-breakers were manufactured in

1954.




Bottom of page 6:

http://www.studiecd.dk/cahiers_techn...evolutions.pdf
 
Real number and real concepts, again taken out of context in relation to the discussion at hand.

You are claiming water will trip an OCPD, even a GFCI all the time- but as your numbers show water and electrode surface area and distance play a role.

you said tap or pool water has very high R and likely not trip a gfci or mccb
I say and PROVE it will with REAL world data and simple computation

they are not MY numbers!!! lol
R = p x L/A are everyones
OBVIOUSLY L and A 'play a role', are you stoned!?!?

I see the light of Jumpers bow out post
I feel a little bad like I'm teasing a kitten lol
 
And concrete among others- why does an unfinished basement need GFCI but not a finished one?

All these areas are places where conditions lower body contact resistance and/or (body) fault path be it concrete, dirt, moisture, grounded object likely to be in reach, ect. In this cases an energized object is very likely to be lethal.



BTW, differential technology existed before Dalziel. Technically he did not invent the device that trips on such a scheme:





Bottom of page 6:

http://www.studiecd.dk/cahiers_techn...evolutions.pdf

MOISTURE!!!!!

MOISTURE!!!!

wrong
he invented and patented it
 
you said tap or pool water has very high R and likely not trip a gfci or mccb
I say and PROVE it will with REAL world data and simple computation

All the videos I posted already did. Even with Clive's salt water electrodes, spaced about 1/4 of an inch apart, about 6 inches long- and on 240- no breaker tripped.



they are not MY numbers!!! lol
R = p x L/A are everyones
OBVIOUSLY L and A 'play a role', are you stoned!?!?

Yes I know- but taken out of context and not the whole picture.

I see the light of Jumpers bow out post
I feel a little bad like I'm teasing a kitten lol

Jumper may automatically take your views without discrimination, but I am not like that.


MOISTURE!!!!!

MOISTURE!!!!

which lowers skin conductivity :D

wrong
he invented and patented it

Then why does my paper say otherwise?
 
All the videos I posted already did. Even with Clive's salt water electrodes, spaced about 1/4 of an inch apart, about 6 inches long- and on 240- no breaker tripped.

Yes I know- but taken out of context and not the whole picture.

Jumper may automatically take your views without discrimination, but I am not like that.

which lowers skin conductivity :D

Then why does my paper say otherwise?

every experiment can be rigged

you do not get it

Jumper does not take MY position, he comprehends the basics, which you do not

really?!?!? it is in series, skin p stays the same
contact R decreases

because it is wrong


now excuse me, I'm wanted back on planet Earth
 
every experiment can be rigged

Yahhh, all 5 You Tube vids are rigged. :roll::roll:

you do not get it

Jumper does not take MY position, he comprehends the basics, which you do not

You spit out numbers which on a few occasions do not tell the whole story as in this case.

really?!?!? it is in series, skin p stays the same
contact R decreases


In simple terms we can say skin resistance at the point of contact is lower.


because it is wrong

A paper by Schneider wrong?
 
OSHA

How does water affect the flow of electricity?

Pure water is a poor conductor. But small amounts of impurities in water like salt, acid, solvents, or other materials can turn water itself and substances that generally act as insulators into conductors or better conductors. Dry wood, for example, generally slows or stops the flow of electricity. But when saturated with water, wood turns into a conductor. This means that anyone working with electricity in a damp or wet environment needs to exercise extra caution to prevent electrical hazards.
 
Yahhh, all 5 You Tube vids are rigged. :roll::roll:


You spit out numbers which on a few occasions do not tell the whole story as in this case.

In simple terms we can say skin resistance at the point of contact is lower.

A paper by Schneider wrong?

yes, Ohm's law is rigged lol

you can't read the equations, hence you miss the whole story

in simple terms, but incorrect terms

inaccurate
 
OSHA

How does water affect the flow of electricity?

Pure water is a poor conductor. But small amounts of impurities in water like salt, acid, solvents, or other materials can turn water itself and substances that generally act as insulators into conductors or better conductors.


Yes, of course, but usually not enough to trip a breaker under the conditions were have in mind in this thread.


Dry wood, for example, generally slows or stops the flow of electricity.


Does it? I wouldn't use it as a hot stick.


But when saturated with water, wood turns into a conductor. This means that anyone working with electricity in a damp or wet environment needs to exercise extra caution to prevent electrical hazards.


Yes, again, conditions that lower skin contact R.
 
250 mA is not gfci
and will kill in < 1/2 sec
6 ma will not

this is more of a leakage detector
but interesting to note it was developed for MINING lol
mines are very WET places

The world’s first high-sensitivity earth leakage protection system (i.e. a system capable of protecting people from the hazards of direct contact between a live conductor and earth), was a second-harmonic magnetic amplifier core-balance system, known as the magamp, developed in South Africa by Henri Rubin. Electrical hazards were of great concern in South African gold mines, and Rubin, an engineer at the company C.J. Fuchs Electrical Industries of Alberton Johannesburg, initially developed a cold-cathode system in 1955 which operated at 525 V and had a tripping sensitivity of 250 mA. Prior to this, core balance earth leakage protection systems operated at sensitivities of about 10 A.
 
anything can be taken out of context or misapplied.


Elaborate. Educate me on what that paper is saying.

yes, or distorted or misunderstood by the interpreting mind
or intentionally and disingenuously by the interpreting mind
lol

can't be done
this thread and the t&d line Z thread are proof
 
[/B]Yes, of course, but usually not enough to trip a breaker under the conditions were have in mind in this thread.

[/B]Does it? I wouldn't use it as a hot stick.


Yes, again, conditions that lower skin contact R.

almost ALL the time
0.2 Ohm is pretty low

it sounds like you've used your noggin'

like all 20 req code locations?

as I said
just yank them out of you house
no purpose or advantage
 
ohm m
pool L = 10, coss section 10 x 2 = 20

pool
R = 0.4 x 10/20 = 0.2 ohm

drinking
20 to 2000
thin puddle
L = 1 mm = 0.001 m
A = 1/4 x 1/4 = 1/2 sq m
R = 20 x 0.001/0.5 = 0.04 Ohm
R = 2000 x 0.001/0.5 = 4 Ohm

all <<<< body Z
you know not of what you speak


Swimming pool water[j]3.33×10−1to 4.00×10−10.25 to 0.30[32]
Drinking water[k]2.00×101to 2.00×1035.00×10−4to

show me why this is not valid?
 
concrete ~ 20 kOhm cm

slab 6" x 20' x 20'
L = 150 cm
A = 370,000 sq cm

R = 20,000 x 150/370,000 = 8 Ohm
pretty low
assume body 800 Ohm, damp floor
rest of path to rod 25 Ohm

120/(8 + 800 + 25) = 144 mA
mccb no trip = dead
gfci = trip and live to fight another day
 