david
Senior Member
- Location
- Pennsylvania
Ok I am going to ask a question and please do not take this thread into a debate about swimming pools
Please not in my example am going to note a detached garage feed from a existing feeder from a single family dwelling
The garage Is existing and is completely code compliant. It has two ground rods connected to the service rated distribution panel
The garage is closes to the swimming pool i need to run a feeder to pool equipment I want to determine if that feeder can be run from the garage or do I have to run it from the service in the dwelling.
The garage supply is 240/120 volts
I need a feeder I am not interested in supplying the pool with branch circuits
(2) Separate Buildings. A feeder to a separate building or structure shall be permitted to supply swimming pool equipment branch circuits, or feeders supplying swimming pool equipment branch circuits, if the grounding arrangements in the separate building meet the requirements in 250.32(B). Where installed in other than existing feeders covered in 680.25(A), Exception, a separate equipment grounding conductor shall be an insulated conductor.
The reference to 250.32 (B) tells me to look at the feeder how is it connected if it is a four wire feeder and connected correctly I can run my feeder to the swimming pool equipment.
If it is not connected correctly it does not meet the requirements of 250.32 (B) I cannot supply my swimming pool from this panel in the garage
If on the other hand I walk up to the existing garage and it is a three wire URD feeder in PVC it doe not meet the requirements in
250.32 (B)
I cannot supply my swimming pool equipment with a feeder from this garage.
When I get back I am going to contrast this to the feeder requirements
In 547.9 (C) in an attempt to illustrate the difference in referencing 250.32(B) in contrast to referencing 250.32
I believe the difference is deliberate and means two different things
ARTICLE 547 Agricultural Buildings
B) Service Disconnecting Means and Overcurrent Protection at the Building(s) or Structure(s). Where the service disconnecting means and overcurrent protection are located at the building(s) or structure(s), the requirements of 547.9(B)(1) through (B)(3) shall apply.
(3) Grounding and Bonding. For each building or structure, grounding and bonding of the supply conductors shall be in accordance with the requirements of 250.32, and the following conditions shall be met:
(C) Service Disconnecting Means and Overcurrent Protection at the Distribution Point. Where the service disconnecting means and overcurrent protection for each set of feeder conductors are located at the distribution point, feeders to building(s) or structure(s) shall meet the requirements of 250.32 and Article 225, Parts I and II.