I can see where the article scope can be interpretted as such... but it does not actually say that it amends Chapter 1 through 4 requirements except as specifically referenced. A statement of such is required by the Manual of Style and must read...
550.13 Receptacle Outlets.
B) GFCI protection. GFCI protection shall be provided for receptacle outlets serving countertops in kitchens,
and receptacle outlets located within 1.8 m (6 ft) of a wet bar sink.
Exception: Receptacles installed for appliances in dedicated spaces, such as for dishwashers, disposals, refrigerators, freezers, and laundry equipment
.
Feeders supplying branch circuits shall be permitted to be protected by a ground-fault circuit-interrupter in lieu of the provision for such interrupters specified herein.
(G) Receptacle Outlets Not Required. Receptacle outlets shall not be required in the following locations:
(2) In the wall space behind doors that can be opened fully against a wall surface
How many times did we here guys ask about how about dedicated rec. to the washer with in six ft of the laundry sink?
What about the space be hind a door on a wall does that need a rec?.
The more I look at it the evidence it seems to indicate that the scoping statement in 550.1 says what it says and that does seem to modify the general requirements of the code. This opinion is not popular here but it is mine
It may not technically match the style Manuel but HUD could have assemble there own panel of experts and written there own electrical standards for manufactured homes. HUD had no interest in the NEC as a Whole they where only interested in the electrical provisions that effect Mobile homes. The scoping provisions in 550.1 seem to wrap this article up in a nice package for HUD to incorporate this article into there standers