Hurk, I really have a problem with your assumptions stated above.
How can you question the usefulness of a rod at the trailer when every other separate structure supplied by a feeder requires a GES?
What I am saying is this .......... I have no idea if the rod is useful or not ........ and neither do you if you are honest with yourself.
But if this did have to go to court how could you possibly argue that a GES at mobile home serves no purpose when all other structures require one. What type of magic does a mobile home have to behave differently?
I also surprised at you having a problem with this view, as much as it has been discussed on here, and in quite a few cases even with documentation? If you are holding this view just because the NEC still requires ground rods, then this goes to show how myths can be held onto just because it is still required, and or passed on, one reason something like this should be removed from the NEC in my view.
Also just because there is a requirement in the NEC does not say it is a scientific fact as we have seen over the years of the changes made when it was proved that something wasn't right, if this was not so, many of the code changes would never be made.
So here is a break down of the myths of a 8' ground rod supposed to do:
Protect a building and its electrical system and its occupants from the effects of lightning.
Here is a post Bryan made back in 2006 on the publish result of a test done that shows very little of the lightning current even followed the path through the rod (which there was 3 of them) to Earth:
http://forums.mikeholt.com/showthread.php?t=77454
The link in the thread to the published paper is dead but can be found here:
http://www.lightning.ece.ufl.edu/PDF/00997942.pdf
It shows that less then 20% of the energy of the triggered strike followed the path to Earth through the rod(s)
As for touch/step potential, stray current/voltage, opening of OCPD's, or anything else that requires passing current through a ground rod, many of us remember the experiments of Crossman Gary who conducted some live experiments that many of us could see that a ground rod was ineffective in reducing or eliminating this hazard, this thread is located here:
http://forums.mikeholt.com/showthread.php?t=116358
As for voltage spike/surges/transients, I cant believe people still think they want to return to Earth, a ground rod does nothing to lower the impact of a surge that is generated usually line to line or line to neutral, it wants to return to source not Earth, even a lightning strike ahead of the utility transformer will be a line to line surge on the house side of the transformer, the transformer isolate the current and it is no longer seeking to return to Earth, this surge would have or should have followed the MGN to the electrode system that is placed every 1/4 mile on the primary system, but once it has crossed a transformer it is no longer reference to Earth because of the isolating effect of a transformer, the same reason a GFP does not function across a transformer.
As for static build up, well if the line was miles long and didn't have other impedances that connected it to Earth like happened in the telegraph lines back when they went to the glass knob insulators, I would agree that they can accomplish this function, but when we have a multi-grounded system that has electrode in every part of the system all connected together, then this need is not there.
I don't want to take this thread sideways any farther but just wanted to answer this post.