if its NM on wood in a bay with glass, where does the TC go? just touching the side of the sheath? under between wood & sheath ??
Id say both, one on one with one on the other.
if its NM on wood in a bay with glass, where does the TC go? just touching the side of the sheath? under between wood & sheath ??
Id say both, one on one with one on the other.
have a read. i suspect my #'s will be close to these, and maybe this info is being used by CEC to change their tables??
The University of Toronto study indicates that the conductors will not be subjected to
objectionable temperatures even under very severe conditions.
http://gfretwell.com/electrical/nema_romex_in_foam_study.pdf
and this doc which basically describes what i talked about in the start of this thread around the heat flux density of wire vs amps. but the free air temps listed are not near where mine were. my amps and TC (temp) seem to be accurate (CM660 accurate), so why the big diffs???
http://loesshillsengineering.com/wp-content/uploads/2015/08/thermal_model_for_wire.pdf
In all the calculations that I do, and most of the papers that I come across, show that #14 is actually slightly oversized (or that number 12 is slightly undersized). #12 appears to get a bit hotter at 20 amps then #14 at 15 amps continuous current. It could be that #14 has a bit of extra safety factor, or just the way the sizes came out when the AWG system was developed leaving #12 a bit small. For #12 to have equal CCC ratios to #14 it would need to be roughly around 3.48mm2 instead of 3.31mm2 as it is now.
so now you are talking about normalizing heat density across the wire sizes. this is something i talked about in this thread. even if you took #14 up to #12 heat density (for its existing ampacity) i dont think #14 temps would climb in ut-oh fashion.
thus far the only "interesting" data seems to be the UL doc that explains (in a formal way) degradation in the dielectric due to physical installation and high temps. the only thing that doc didnt show was insulation degradation of under the UL listed temp vs time vs degradation. it says they accelerated aging but do not define what that aging graph looks like, so not very clear how their aging process maps back to say a #14 NM that runs at 12A on continuous load for say 12 months.
my test will simply show the temps. what has to follow, either by using existing data or obtaining new data, is how these temps pose a hazard (if any) over time.
a couple of pics before i get on the horn with Omega
the TC installation is rather straightforward, they are in a shallow channel and the tips contact the wire. the other pic simply shows how i terminated the end of the NM, basically using eyelet lugs that are bolted together and then the whole thing soldered, to reduce any ohms there thus reducing heat generation at that junction point.
![]()
![]()
ok, Omega TC connectors are on their way ($1.50ea, $8 to ship, go figure), and i ordered a bag (50) of Wago 222-412's, i can cook these later
and just me re-visiting what i said a few posts back about free air temps, i may be wrong, those other tests might have been NM with two CCC's in free air, not a single wire like i had tested. so, its all good data but not all in same context, etc. i think we can say the amps ability of just a single wire in THHN/THWN (free air) is well above any ampacity #'s NEC has while staying below wire rated temp, but this does not represent any proper use of NM in real world, etc. i'll cook a piece of NM in free air now.
the sandwich test will reveal better data.
And, one last request, NM stapled to wood without anything. This will give 4 real world examples of heat dissipation.
The wago is for dessert.![]()
just so we have another reference for data, this is 24" (48" RT) of the same NM wire, cooking at 15A now, it has to cook for about 1hr before i'll record the temp. the TC is on the wire in a way that would be NM laying flat-horizontal, so we can see what the temp might be from two CCC's giving up heat where that energy heats the top wire more, etc. ambient today is 60F.
![]()
from what i saw, it was 10F for 10F, thats +10F ambient = +10F wire temp. we can add 30F to this specific test. i have not run the math for this 10-for-10 but its what i saw between 60 & 70F ambients. if anyone can confirm the math that would help.Very cool
Technically the NEC would let you go higher being 60*F, but lets see what this amounts to first.
.i can only do one test of NM in a bay w/ glass and covered like a real wall, and one test of it just on wood (i assume you mean free air)
this is an important factor to note (the "one" test) because installation characteristics play a role. as example, i may get the NM to not lay perfectly flat against the wood and this will skew the #'s slighlty because the heat dissipation will be different vs another install where NM is laying perfectly flat on the wood. this type of test, as was done in that UL test, needs a repeatability component to obtain a set of data per test, which is something i cant do currently.
so as of now, the tests are/were:
all #14 btw
1) a piece of bare copper wire from NM tested in free air - done
2) a piece of insulated copper wire from NM tested in free air - done
3) a piece of full NM in free air - TBD, cooking now
4) a piece of full NM in rigid foam sandwich - TBD, waiting on Omega connectors
5) a piece of NM in a 2x R13 glass sandwich - TBD, need to get glass
6) a piece of NM in a bay on wood w/ glass and bay finished like a typical ext wall of a home - TBD, need to build it
7) a piece of NM on a piece of wood (or maybe this is #6 but w/o the glass?) - TBD, need to build it
8) wago 222 tests - TBD, waiting on 222's to arrive
from what i saw, it was 10F for 10F, thats +10F ambient = +10F wire temp. we can add 30F to this specific test. i have not run the math for this 10-for-10 but its what i saw between 60 & 70F ambients. if anyone can confirm the math that would help.
where does NEC get 86F(30C) anyways?
having a set # seems odd given all the allowed uses of NM where ambient can way higher and lower. how would i know what to pick for ambient when attempting to derate a wire?
today my outside temp is 70F, the NM in my 6" non-insulated wall might be 85F because sun hitting that wall today is heating the bay, but in dead summer the temp in that bay might be 130F, dunno, are there std's based on zones and sun exposures?
IRBC in some sections breaks up criteria based on zones, and in some cases for wind calcs have coefficients for surroundings (nearby buildings, trees, etc etc). if we derated NM for my home, especially where all of the service panel BC's exit the panel into the bay i am talking about, #14 would likely be derated so low a 15A ocpd would be too big, and #12's would all have to be on 15A ocpd's.