Tested all of the receptacles, and all tested correctly.If you have a L/N reversal it would show up on any given 120V receptacle with one of those plug in testers on the line that is reversed. Simple point to test would be to set up a temp receptacle at the panel, and test with your known correctly wired receptacle. If one of the lines is reversed it would be evident there.
If you have amperage back feeding on neutral you should be able to read that with mains turned off as reading from N/G.
If the issue presents specifically at a specific time of day you may have a utility issue (substation switching etc) or loads from another upstream customer that comes on at a specific time.
where about in PA? not too far from PA.
The house around Milford PA.