Picture worth a 1000 words ?
Picture worth a 1000 words ?
To make the negative 1 Power Factor a little clearer look at the attached picture.
When 1000 Watts is flowing in from POCO at unity PF the Watt Meter reads 1000 watts & the PF meter points straight up 12 0'clock. If 1000 VARs are flowing reactive the PF meter points to the 9 o'clock position "0" and the watt meter reads zero also.
When 1000 watts of power flows back toward POCO the the PF meter points to the 6 o'clock position which is sometimes refered to as negative unity or a negative 1 PF. The wattmeter would now read 1000 watts again.
If you only apply voltage to the meter it spins round & round & round like a synchro-scope.
Picture worth a 1000 words ?
To make the negative 1 Power Factor a little clearer look at the attached picture.
When 1000 Watts is flowing in from POCO at unity PF the Watt Meter reads 1000 watts & the PF meter points straight up 12 0'clock. If 1000 VARs are flowing reactive the PF meter points to the 9 o'clock position "0" and the watt meter reads zero also.
When 1000 watts of power flows back toward POCO the the PF meter points to the 6 o'clock position which is sometimes refered to as negative unity or a negative 1 PF. The wattmeter would now read 1000 watts again.
If you only apply voltage to the meter it spins round & round & round like a synchro-scope.