Bobby: You are consistently missing the point and you cannot adequate explain HOW the earth plays a part in clearing faults within a structure with distribution under 600 VAC.
bobby ocampo said:NEC requires it to be connected to ground for the reason that it will reduce the potential of an accidentally energized metal piece to ground potential and therefore reduce electric shock hazard. Otherwise NEC would have removed it a long time ago.
Proof of this is is in a single line-to-ground fault in an ungrounded system or HRG SYSTEM.
Bonding without connection to the reference plane will still have a an electric shock hazard. This is the reason and the PHYSICS behind why NEC requires it to be connected to ground through a ground rod or other acceptable means in the NEC.
peter d said:So again I ask, how do we accomplish this all important connection to earth in a ship or an airplane? The structure of a ship or plane and EGC's are bonded to the source neutral and never connect to dirt.
bobby ocampo said:If grounding and connection to earth is not important then NEC should have a long time ago removed this requirement.
brian john said:Then what would you do in regards to lightning and primary to secondary faults with in the utility transformers?
There are reasons for this connection to earth JUST not the horse you are beating to death.
brian john said:Bobby: You are consistently missing the point and you cannot adequate explain HOW the earth plays a part in clearing faults within a structure with distribution under 600 VAC.
bobby ocampo said:...Connecting to earth is to reduce electric shock by reducing the potential of the energized metal piece to ground potential...
tryinghard said:Do you think potential is affected by resistance?
bobby ocampo said:Please clarify what you mean by your question Sir.
True, but then, when is the last time you were able to touch a hot electrical conductor on a ship or a boat while standing on earth?peter d said:The structure of a ship or plane and EGC's are bonded to the source neutral and never connect to dirt.
We all know that resistance is futile.tryinghard said:Do you think potential is affected by resistance?
LarryFine said:We all know that resistance is futile.
tryinghard said:If you have one potential value within 1' of your grounding electrode will you have the exact same potential value at 6' from the same grounding electrode?
bobby ocampo said:Sorry Sir, Still don't get what you are driving at?
Connecting to earth is not for clearing the fault. Connecting to earth is to reduce electric shock by reducing the potential of the energized metal piece to ground potential. In an ungrounded system the OCPD will not clear the fault in a single line-to-ground fault to have continuity of service. Industrial Power System Handbook by Beeman. However Equipment grounding is important to reduce the potential of the accidentally energized metal piece to ground potential not clear the fault.
Connecting to earth is to reduce electric shock by reducing the potential of the energized metal piece to ground potential
tryinghard said:Do you think potential is affected by resistance?
bobby ocampo said:Please clarify what you mean by your question Sir.
tryinghard said:If you have one potential value within 1' of your grounding electrode will you have the exact same potential value at 6' from the same grounding electrode?
I?m really not driving I?m asking you a poignant question.bobby ocampo said:Sorry Sir, Still don't get what you are driving at?
bobby ocampo said:Sorry Sir, Still don't get what you are driving at?
With the exception that GFCI's would neither function nor be necessary to protect someone standing on the earth while contacting a hot wire.brian john said:I could totally isolate the building from earth and and the system would work exactly the same.
LarryFine said:With the exception that GFCI's would neither function nor be necessary to protect someone standing on the earth while contacting a hot wire.
It doesn't have to be 'dirt' per se, but there has to be a connection between one circuit conductor and whatever coductive surface (i.e., the aforementioned 'ground plane') one might contact while making accidental contact with the other (i.e., the 'hot') circuit conductor.jim dungar said:Larry, GFCIs do not need a ground reference to function. If there is not a complete circuit then current will not flow and the GFCI will not trip, but it is not because there is no dirt. GFCIs function just fine in my wooden floor kitchen or on the 25th floor of a high rise, neither of which have dirt in their fault path.