Incorrect back at you.Incorrect.
OK, I agree with all of the above, but it has no direct bearing on the issue. Using the grounded conductor terminal bar is one way to connect the EGC to the grounded service conductor and complies with the above language.250.130(A) specifically states "The connection shall be made by bonding the equipment grounding conductor to the grounded service conductor and the grounding electrode conductor." The grounded service conductor ends at its termination to the grounded conductor terminal bus. The bus does not extend the service conductor.
Show me something in Article 250 that says that the 250.130(A) EGC to grounded service conductor connection can't be made that way. Or that removal of the Main Bonding Jumper has to sever all connections of the EGCs to the grounded service conductor.
I don't believe there is any such language, so the practice is permitted.
Cheers, Wayne