That is not how they work. They work by some fancy (proprietary) algorithm that looks at an arc signature. To minimize false trips they do no look for an arc signature of a parallel arcing fault unless the current exceeds 75 amps. They are designed to detect arcing faults which they claim are responsible for the majority of dwelling unit fires.
Many others claim that the majority of dwelling unit fires are caused by joule heating at a poor connection, something an AFCI without
a GFP circuit does no better at detecting and clearing than does a standard thermal magnetic breaker.
Ok then , since you are at least trying make a constructive claim. You say, "They work by some fancey proprietary algorithm " is boloney . They work similar to a GFCI breaker . The GFCI breaker sences line to neutral load and trips with any unbalance 5 to 6 ma . AFCI works in a similar fashion. It will trip at 30ma when the available fault current is too low (could be 75amp level?) to clear the fault preventing an arcing condition
that leads to a fire. A thermal magnetic breaker will not respond fast enough at 500% 5sec to long to extinguish an arc