Gentlemen: kindly refer to Table 210.21(B)(2) and 210.21(B)(3). A 15 amp duplex receptacle is allowed on a 20A circuit, BUT you are only allowed to plug a 12 amp load into it. You will find that Listed utilization equipment with a 15A attachment plug will have a current rating of not more than 12 amps.
Gentlemen: kindly refer to Table 210.21(B)(2) and 210.21(B)(3). A 15 amp duplex receptacle is allowed on a 20A circuit, BUT you are only allowed to plug a 12 amp load into it. You will find that Listed utilization equipment with a 15A attachment plug will have a current rating of not more than 12 amps.