James L
Senior Member
- Location
- Kansas Cty, Mo, USA
- Occupation
- Electrician
I get your beef, I really do. I did a service callthe other day, pulled a recep out of the wall and a backstabbed neutral came out of the back. It does happen.All i've done is residential/commercial service work for 20+years. I've seen hundreds, if not 1000's of burnt up receptacles. Due to backstabbing (mostly (not the installers fault), screw not ever tightened (next most frequent, installers fault), and the devices just plain failing internally. What it comes down to is I'm against using residential 15 and 20 amp receptacle devices and pass-thru power. That is the crux of my beef. I have 3 yrs to propose this it seems if I can find the time.
But screws also become loose over time. And whether it's a spring loaded connection or a screw, loose is loose. Plug a space heater into a recep that has a loose connection, and the least of your worries will be whether the other receps stop working.
I've seen just as many burnt wires on screw terminals as I have backstabbed ones. And that's irrespective of how many wires are connected.
Google - "burnt electrical outlet" and click on the images tab. Many of them show screw terminals that have burned
Breaker screws loosen, netral bar screws loosen, and recep screws loosen.