From Wiki (Tesla forgive me)
Fixed appliances on three-wire circuits[edit]
In North America, the cases of some kitchen stoves (ranges, ovens), cook tops, clothes dryers and other specifically listed appliances were grounded through their neutral wires as a measure to conserve copper from copper cables during World War II. This practice was removed from the NEC in the 1996 edition, but existing installations (called "old work") may still allow the cases of such listed appliances to be connected to the neutral conductor for grounding.
This practice arose from the three-wire system used to supply both 120 volt and 240 volt loads. Because these listed appliances often have components that use either 120, or both 120 and 240 volts, there is often some current on the neutral wire. This differs from the protective grounding wire, which only carries current under fault conditions. Using the neutral conductor for grounding the equipment enclosure was considered safe since the devices were permanently wired to the supply and so the neutral was unlikely to be broken without also breaking both supply conductors. Also, the unbalanced current due to lamps and small motors in the appliances was small compared to the rating of the conductors and therefore unlikely to cause a large voltage drop in the neutral conductor.