Residential Wiring

Merry Christmas

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
I remember the days of installing one GFCI circuit per house, it was code compliant.
Electricians are appalled at that now, but I was recently in one of those early '90s homes to troubleshoot an exterior receptacle on the back of the house.

I expected to see at least the master bathroom separated from all the rest, but it wasn't. There was only one circuit. Front and rear receptacles, two in the garage, one in the basement, and four bathrooms.

I asked the owners if they ever had any problems with overloading that circuit. They said they couldn't remember ever having that breaker trip in 8 years living there
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
It says your an instructor in Florida, if I am not mistaken for the last decade (since 2014) its been in the FECC section C405.7.3 states that feeders are to be sized for a maximum voltage drop of 2%, Branch circuits are under FECC C405.7.3.2 are 3% so I would say its not accurate to say the Florida code omits voltage drop, its just not in the scope of the National Electrical Code to even address the topic so it went in a different code.
I was referring to residential installations. I think the FECC refers to commercial buildings.
 

drpcfix

Member

drpcfix

Member
I live in a single family home in a gated community in south FL. House was built in early 80's. Two front bedrooms, lights and outlets along with all outdoor lights and outlets were wired on one 15a breaker with #14.

Planning a major rebuild which will include having all that ripped out. 1 15a per room for lights and 1 20a per room for outlets is what I like. Plus a separate subpanel for the kitchen.

House doesn't even have a main breaker.

Got 4 breakers at top of panel, 1 each for hw, ac, dryer and heat plus 2 60a, one for each half of the rest of the panel all wired directly to the meter.

Its worked fine all these years but with the addition being added and 2 EVs and generator plus new arc fault requirements going to all need to be replaced.

Im thinking 200a transfer switch to main panel in new garage with all the 240 loads in there plus a new subpanel where the original one was, plus another sub for the kitchen and another for the pool.

Will use load management on all the heavy hitters to meet the 158a limit on the generator. That along with heat pump for ac, hw and pool heat/cool.

As a note, EV only gets used in middle of night.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Got 4 breakers at top of panel, 1 each for hw, ac, dryer and heat plus 2 60a, one for each half of the rest of the panel all wired directly to the meter.
Sounds like a split bus panel. I wouldn't even attempt to add to it. Adding such large loads will cause issues on the old bus and to have in most cases catastrophic failures. Recommend to customer replacing with new panel.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
drpcfix please update your profile to show your occupation and location.

Thank you
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
A separate lighting circuit in each room in a residence is foolish, but each bedroom on their own circuit is not a bad thing.
I've done that in some retirement communities, with each room having a 20 amp circuit for receptacles. Then a lighting circuit or two throughout.

I just think a retirement home is a lot more likely to have the demand of a space heater or oxygen concentrator, et al
 

Frank DuVal

Senior Member
Location
Fredericksburg, VA 21 Hours from Winged Horses wi
Occupation
Electrical Contractor, Electrical Engineer
His question was ...........how many receptacles can he put on a 15 amp circuit.
Multiple the square footage of the dwelling times 3 VA per square foot.
Divide that by 120 volts.
Then divide that by 15 amp circuit breakers that you will need.
Round up if you have a remainder (fraction thereof).
That's a real minimum, not something I would EVER wire to. I am not in the cheapest way is my way. I hardly ever wire 15 amp receptacle circuits. 20 amp AFCI/GFCI breakers cost the same, and I feel better having more receptacles. Not that silly 12 foot rule (so a lamp with a 6 foot cord can fit most anywhere, but then there is if it sits on a table, then you have to account for drop to floor length....;)). i.e. I do not wire a house to a specification I would not want to live in!

Using that formula, a 3000 sq ft house only needs five 15 amp breakers (plus laundry, kitchen). Wiring to the 50's idea of 4 circuits in a house on a 60 amp service still?:unsure:

And why the licensed electrician remarks? Trying to insinuate all licensed electricians are the same? :LOL:
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I typically wire receptacles and lighting separately, and also prefer 20a for receptacles and 15a for lighting. I agree with the reasoning of bath and kitchen lighting staying on during an appliance malfunction.

Even if every bedroom has its own 15a circuit, turning on the lights to vacuum is likely to trip a 15a breaker, but one 20a circuit can supply several bedrooms because you're only going to vacuum one room at a time.

Also, lighting and fans are relatively known and fixed loads, so it's easier to load lighting circuits efficiently with little risk of overload. Receptacles can be asked to supply almost anything unpredictable over time.
 