170527-1853 EDT
Smart $:
Power factor is only meaningful as applied to a two terminal load. The definition is PF = W/Eeff*Ieff from "Analysis of AC Circuits", p 28, Melville B. Stout, Professor of Electrical Engineering, University of Michigan, 1952.
A quote from Stout on p 28 "From a laboratory standpoint, power factor is the same for distorted waves as for pure sine waves -- it is the quotient obtained by dividing the wattmeter reading by the product of voltmeter reading by ammeter reading." Obviously from my first paragraph RMS values are implied.
One can extend the definition of power factor from a two terminal device to a balanced three phase load if appropriate voltage and current measurements are used.
The input power factor to a device or system that goes from AC to pure DC and then to something else as the final load were the DC load power and voltage are constant, and that final load has an arbitrary power factor will not have its input power factor affected by the final load power factor. That constant DC bus isolates the input power factor from the final output factor. However, changing the DC load power can change the input power factor.
.