If I lost power coming into the building, how will 6-7 banks of single phase inverters recreate the 3 phases? Could they be self starting and create the 3 phases correctly timed?
If I lost power coming into the building, how will 6-7 banks of single phase inverters recreate the 3 phases? Could they be self starting and create the 3 phases correctly timed?
Grid following inverters can never do the above. PV inverters are often grid following only.If I lost power coming into the building, how will 6-7 banks of single phase inverters recreate the 3 phases? Could they be self starting and create the 3 phases correctly timed?
Correct, but this is true of basically any PV inverter that is not also a battery inverter.Thanks. Battery system will be in another building with 3 phase inverter. If it failed, or was disconnected for some reason, then the 24 individual inverters cannot continue to operate in 3- phase mode, correct?
I don't know what else I can tell you; it works, and VA in = VA out. Does this help?So far, I can see how the formulas and graphs presented for the RESULTANT as seen by a load on A-B works. I can see how an inverter can send back the resultant waveform and provide the same power to an electric stove, or water heater. But, I cannot see that single waveform being effective to replicate those two waveforms going backwards into the two coils of the transformer.
I do appreciate all the comments and the effort to help me grasp this complex situation. I understand the resultant waveform for the two A-N and N-B passing through a load to get A-B.
I don't understand how pushing the resultant backwards provides the same results in the two coils A-N, N-B.
But you just told him the line currents and he's struggling to understand how the line-neutral voltage is maintained.I don't know what else I can tell you; it works, and VA in = VA out. Does this help?
Ia = sqrt(Iab^2 + Ica^2 + (Iab)(Ica))
Ib = sqrt(Ibc^2 + Iab^2 + (Ibc)(Iab))
Ic = sqrt(Ica^2 + Ibc^2 + (Ica)(Ibc))
OK, but L-L voltage is L-N voltage times sqrt(3), and the inverters match what they are connected to. Once again, I encourage the OP to study the fundamentals of three phase power.But you just told him the line currents and he's struggling to understand how the line-neutral voltage is maintained.
If the single phase inverters are connected line to line, it is essentially a delta to delta connection. Does that help or make it worse?Ggunn basically he is asking how it's possible to backfeed a wye grid with a delta inverter. We know it works. Can we explain exactly how? (Even if he doesn't need to understand it know it will work.)
Yes, A-N can stay 0, and if A-B = N-B as you've correctly stated, it must be zero. When we define voltage between two points, the resulting values have to satisfy certain rules. The most fundamental is that adding up the voltages around a loop is always 0. So for voltages, A-B = N-B + A-N, always. When A-B = N-B, that leaves us with A-N =0.I don't understand how pushing the resultant backwards provides the same results in the two coils A-N, N-B. At time zero, the resultant voltage A-B is 120V*sqrt(2)*sin(120 deg), A-N wants to be 0, and N-B is 120V*sqrt(2)*sin(120 deg). How can A-N see anything but 120V*sqrt(2)*sin(120 deg) volts and have electrons moving in the same direction and velocity as the resultant A-B? A-N cannot just stay at 0.
I think you may be misapprehending the difference between voltage and current. With a grid-following inverter, the voltages in the entire system are determine by the grid (or in a blackout, by a grid-forming inverter elsewhere in the system). All of your discussion earlier in your post was just about voltage waveforms, and how they are related A-B, N-B, and A-N.So far, I can see how the formulas and graphs presented for the RESULTANT as seen by a load on A-B works. I can see how an inverter can send back the resultant waveform and provide the same power to an electric stove, or water heater. But, I cannot see that single waveform being effective to replicate those two waveforms going backwards into the two coils of the transformer.
The same way a wye grid can supply a delta connected load, just with a minus sign on the currents?Ggunn basically he is asking how it's possible to backfeed a wye grid with a delta inverter.
The same way a wye grid can supply a delta connected load, just with a minus sign on the currents?
Cheers, Wayne
Pretty sure that if you have a delta source and connect it to the wye side of a transformer, the center connection point of the wye will become a neutral point of your delta, and you can derive a neutral that way. [Edit: maybe that's only for the wye-delta case. This requires some more thought.] Not clear on what advantage the zig-zag has for this application; perhaps there is some serious problem with deriving a neutral this way.He is correct that if you have *only* a delta source present and feed it into the wye side of a typical wye-wye or wye-delta transformer, the transformer does not create a wye. (Only a special transformer like a zig-zag could do that, right?)
Well, the voltages in the system are set by the primary source, the backfeeding grid-following inverter doesn't change any of the voltages. So the L-N loads see the same voltages with or without the backfeed.Or to rephrase how I put it ggunn: can we explain how line-neutral *loads* still get the right voltage and current when you backfeed a wye system with a delta source?
Pretty sure that if you have a delta source and connect it to the wye side of a transformer, the center connection point of the wye will become a neutral point of your delta, and you can derive a neutral that way. [Edit: maybe that's only for the wye-delta case. This requires some more thought.] ...
I'm not sure precisely what you are driving at, but if you connect a delta source, e.g., an inverter without a neutral, to a a wye service or transformer secondary with a grounded neutral, the neutral provides the zero V reference for the phase voltages, and the inverter needs to reference it as well, but obviously a delta source has no neutral. In practice a three phase inverter can either have a neutral connection back to the service or transformer, or there can be a grounded "neutral" at the inverter, but obviously not both; running a neutral to a neutral agnostic inverter would be a waste of money, so I don't do it unless a customer wants it for some reason.Pretty sure that if you have a delta source and connect it to the wye side of a transformer, the center connection point of the wye will become a neutral point of your delta, and you can derive a neutral that way. [Edit: maybe that's only for the wye-delta case.
This is an aside from the OP's scenario: say you have an (ungrounded for simplicity) 480V delta 3W service from the utility, and you have a transformer with a 480Y/277V primary, so you hook up your 480V 3W delta to H1-H3, and leave the secondary disconnected. Can we use H0 as a neutral point and power a 277V load using it? And does the answer depend on whether the secondary is a wye or delta?I'm not sure precisely what you are driving at
I think that if you had two single phase grid-forming inverters connected A-B and B-C, and they had the firmware and connection to talk to each other and sync their voltage waveforms to be 120 degree apart, effectively acting as an open delta source, then depending on the answer to the previous question, you could get a neutral point.But I think we agree that you don't get the neutral point if you have only one single phase inverter feeding that transformer with no other source present. (Or two on different phases, for that matter.)
I don't think that the scenario is so precisely defined in the OP's posts. My latest read is that the OP thinks the single phase inverter has to somehow recreate the voltage waveforms A-N and N-B all on its own, which is never true for a grid-following inverter.He keeps presenting us with that scenario, and we keep having to say that won't be all that's going on.