Art 100 definitions:
Where does it say a MWBC becomes two separate circuits after it effectively splits into two separate circuits? The whole thing is still one (multiwire) branch circuit.
Service and feeders have nothing to do with these definitions.
Branch Circuit. The circuit conductors between the final overcurrent device protecting the circuit and the outlet(s)
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.
Where does it say a MWBC becomes two separate circuits after it effectively splits into two separate circuits? The whole thing is still one (multiwire) branch circuit.
Service and feeders have nothing to do with these definitions.