How does one evenly proportion that which is unknown?210.11 (B) Load Evenly Proportioned Among Branch Circuits
How does one evenly proportion that which is unknown?210.11 (B) Load Evenly Proportioned Among Branch Circuits
You cannot. Just more useless code language.How does one evenly proportion that which is unknown?
Reasonable division is something that someone can claim to do but it is cannot be done without knowing the future loads. I think that we all try to divide the receptacle/lights up evenly but it doesn't really ensure that loads will be evenly distributed. I'll stick with my assessment in post #62.Exactly how to do this proportioning is IMHO not well clarified. Say you've calculated that you need 3 general purpose circuits. Do you proportion these circuits by number of outlets, or do you proportion these circuits by associated floor area? But with any reasonable installation you can come up with a reasonable division of the circuits and be just fine.
When countertop receptacle spacing changed (maybe 15-20 years ago, I don't remember) there was a very solid EC that misread the requirement and did a few houses with the receptacles no more than 2' apart. I was inspecting them and let him know....Every so often, in inspecting, I would have a DIYer interpret the "six foot rule" as a receptacle every 6 ft.
How are they lighting outlets? The term lighting outlet is a defined term and does not include receptacles. The general use receptacles are included in the 3VA per square foot calculation which includesThe receptacles in a dwelling for the most part are "lighting outlets" even the bathroom receptacle is in this portion although minimum size for it is 20a and is doesn't cover a large square footage
I agree. I don't know any way in an existing home to set up an office with multiple computers, monitors, printer, and desk lighting, or a home recording studio with lots of very small loads, or a home entertainment system with multiple components without using power strips.No matter how many outlets you have, it always seems like you need more and end up with a bunch of power strips. While I am not a huge fan of power strips, I don't believe they are fires waiting to happen as a lot of electricians like to claim.
Bath lights can be on with the receptacle so long as it's dedicated for that bath. In a 60a service they were in the lighting section.How are they lighting outlets? The term lighting outlet is a defined term and does not include receptacles. The general use receptacles are included in the 3VA per square foot calculation which includes
- (1)All general-use receptacle outlets of 20-ampere rating or less, including receptacles connected to the circuits specified in 210.11(C)(3) and (C)(4)
- (2)The receptacle outlets specified in 210.52(E) and (G)
- (3)The lighting outlets specified in 210.70
Also pre 2020 nec the 3 va per ft was in table 220.12 that 3va included all that you listed. The general outlets are or were "lighting load" outletsHow are they lighting outlets? The term lighting outlet is a defined term and does not include receptacles. The general use receptacles are included in the 3VA per square foot calculation which includes
- (1)All general-use receptacle outlets of 20-ampere rating or less, including receptacles connected to the circuits specified in 210.11(C)(3) and (C)(4)
- (2)The receptacle outlets specified in 210.52(E) and (G)
- (3)The lighting outlets specified in 210.70
Ach well heaven forbid, tech HO how to install an outlet and tighten wire nuts and leave HO the outlets with pigtails and outlet plates.not happy with the number of receptacle and he does not want to approve the work.
TOTAL VA load for dwelling is outside diameter sq ft x 3 VA
So calculating the number of 20 ampere circuits would still be:
Total square feet x 3 VA / 120 x 20 branch circuit
However, after looking at my book it says that determining the number of receptacles allowed on one circuit would be 120 x 20 / 180 VA for NON DWELLINGS so you are right
Which means besides the 6 -12 foot spacing requirements I guess I do not know how many receptacles can be placed on a 120 v x 20 i = 2400 VA branch circuit for dwellings?
Does anybody know?
Agreed I dont think its super complicated or special, 220.11 says the branch circuits are calculated per 220.10.In WA you need to calculate the square footage that is covered by the lighting calc so 1 circuit per 600ft^2 or so.
I would judge the branch circuits by two factorssingle family home 3300 sq ft, 4 bedroom two story. The owner has about 160 outlets.
But same va per ft either way is requiredMore smaller rooms require more receptacles than fewer larger rooms due to more wall space.
I agree and the NEC uses the word load not receptacles.
Receptacle outlets aren't loads.