I know...I know!!! 220/221 wired it! That's the problem right there!

Hey!! If I wanted this kind of abuse I would have stayed married!


You thought I would never venture into an education forum huh?

Fockers!
 

PaTerminator

Member
Location
Lehigh Valley PA
Occupation
Electrical Contractor
mwbc???

mwbc???

It would seem that circuits 2+8 / 9+18 / 15+24 / 25+35 / 28+34 are all multiwire branch circuits. However, I don't see losing 5 neutrals at the same time very likely.
 

quogueelectric

Senior Member
Location
new york
I for one am not buying these voltage measurements. It would be impossible unless some of the breakers are tripped and or not working. There is something rotten in denmark and I am calling 480 out on the carpet to refute asap.
 

220/221

Senior Member
Location
AZ
It would seem that circuits 2+8 / 9+18 / 15+24 / 25+35 / 28+34 are all multiwire branch circuits. However, I don't see losing 5 neutrals at the same time very likely.

Maybe the neutrals were terminated on a section of neutral bus that was bad/loose?
 