and much easier to test breakers.
That is the thing, they were not testing breakers they where putting on a show.
and much easier to test breakers.
That is the thing, they were not testing breakers they where putting on a show.
I could be misinformed. I will say I have not seen anything on this in Wikipedia either.QO does not stand for Quick-open and never has (regardless what you see on Wiki-pedia).
The family series was QO, Q1, Q2, and Q4, which replaced previous families of breakers like XO, A1, MO and others.
Some QO breakers, in the 15A and 20A 1-pole size, do have a Qwik-Open (R) feature which provides for a 'faster trip' than standard QO breakers (I believe a low pickup point plays a role in this). I would have to check my old product data sheets, but I recall that the Qwic-Open was not part of the original product release.
The breaker test kit ran at 120VAC which is one reason is was discontinued. One version contained bus connections for breakers and a standard duplex receptacle. The demo was to insert a paper clip into the receptacle and then see what happened. A seond version included an air core inductor (about 250' of coiled #18AWG) which allowed for a sparking test. The test set instructions recommended that an extension cord always be used to limit the current so that the building branch breakers would not trip. This effectively prevented most breakers from entering their magnetic pickup points. Another trick we often used was to keep the competitors breakers cold, while ours were kept warmer.
Do you have information on what QO stands for if that is not it, this has been what I have known almost my entire career, but like I said I could have been misinformed a long time ago and never found out any different.
For an A/C Unit above an Gas station I was considering using an used three pole 40amp FPE stabloc breaker... any comments on reliability of used breakers? Thanks in advance!
I would never use a used/untested breaker. A little breaker like that costs more to properly test than to replace. There are new replacements available on the market but depending on the condition of the panel replacement or the CH retrofit may be the better option.
Many of those old panels were in narrower cabinets then today's standards, combine that with the high use of twins, thins or tandems that was popular and you easily get a pretty crowded panel, I don't think I would want to put in the CH retrofit on most any of those older small cabinet applications, just not enough space in the cabinet.I would never use a used/untested breaker. A little breaker like that costs more to properly test than to replace. There are new replacements available on the market but depending on the condition of the panel replacement or the CH retrofit may be the better option.
We needed you!
I have to ask, how are the new FPE replacement breakers? Such as those made by UBI, ect? Do they still have the same issues?
We needed you!
I have to ask, how are the new FPE replacement breakers? Such as those made by UBI, ect? Do they still have the same issues?
For an A/C Unit above an Gas station I was considering using an used three pole 40amp FPE stabloc breaker... any comments on reliability of used breakers? Thanks in advance!
What is this test ?
QO vs FPE ?
Is there a link some where ?
No link. Its a do it yourself. With PPE, Take an 15 or 20 amp FPE breaker run it through a QO. Short the wire. Qo trips fast. Then do the same thing minus the QO in series. Watch and learn. To those who aren't convinced they change their opinion quick:happyyes: