post # 77 & 78, what do these files do ?
posts #50 & 81, after PM, please post response for run at 3%, not 3 volts.
The voltage shown is the L-N voltage drop; in volts not in %.
That's what mV/A/m gives you.Using 3 Volts, rather than 3% is Transformer independent.
That's what mV/A/m gives you.
They are values given in BS7671.Can you share your work, so we can see how the variables are used?
They are values given in BS7671.
For example 16mm^2 is 2.8mV/A/m.
You know the current, the length of run, so simple multiplication gives the voltage.
As I said, I'd be surprised if you guys don't have something similar.For those less fortunate, without a copy of BS7671, can we see your work.
As I said, I'd be surprised if you guys don't have something similar.
Anyway, there isn't much calculating. If your 16mm^2 was carring 10A it would be 2.8mV/m etc.
Simple innit?.............
And you can get conversions on the internet.
Convert gives you a wide range of choices.
208vac to neutral is a rare transformer used in older commercial & industrial buildings.
240V Split Phase Delta, or High Leg Delta, where #C Leg (Orange) of 208vac to Neutral is also called a Stinger leg.
While VD% changes dramatically between 3Ø 120vac vs 3Ø 208vac, both L-N calcs get 3.08 Volts @ pf 0.85 166ft.
Using 3 Volts, rather than 3% is Transformer independent.
I thought you must.if our #12 (1.7 Ohm/th ft) were carrying 10 A
v drop = 17 V/th ft
we do have something similar
the NEC table
I thought you must.
And simpler than your last post.
I think most of our members would have understood that.the BS is not simpler, nor is the NEC, they are IDENTICAL
I think most of our members would have understood that.
You may have inferred that. Incorrectly if I may say so.not sure about that
you implied they were different and the BS std was simpler