You are not making any sense here.
My statement was that if you reduce branch circuit current the neutral current will decrease.
You say that is false, please elaborate.
You are not making any sense here.
My statement was that if you reduce branch circuit current the neutral current will decrease.
You say that is false, please elaborate.
I have upgraded services on some of those when they added AC.
Same here, but most of those same schools now have AC in at least portions of the buildings, though most are seeing AC nearly everywhere.
The small school districts around here share a school nurse. They only are there long enough to perform some basic physical exams once a year on each student, and the room they use for that is vacant most of the time otherwise. If a child gets sick or injured during school a teacher or other staff may stay with that child until parent arrives to pick them up, unless it is something serious enough then an ambulance may be called, and parent is directed to meet them at hospital. Many small schools do have someone that is a volunteer EMT on their staff, not that they seek them out, it just happens that way in small towns.
When I was in school there was a nurse there, maybe not full time but quite often. But that wasn't exactly yesterday. Today at the schools in this region you will almost never see one. Maybe different in bigger towns/cities but not in the little schools in these towns with less then 1500 population. They come in only once or twice a year and check vision, hearing, and other basic physical examinations of students, and are seldom ever seen otherwise.The schools I went to had a full time nurse on deck, so I guess it really does vary by location.
The third harmonic content from each phase in a three phase system adds in the neutral. That's what happened.
It isn't actually what you stated nor what I claimed you posted was incorrect.You are not making any sense here.
My statement was that if you reduce branch circuit current the neutral current will decrease.
You say that is false, please elaborate.
I gave a response to mbrooke's point.Actually struck me as quite funny when you put it like that. Given how smart Besoeker is it struck me as funny picturing him saying something like that, which he does not support but seemed to just by what he wrote.
I know. You were talking about one thing and Iwire another. Iwire took it to mean you were saying reducing the total load would not subsequently reduce neutral current. Just struck me as funny this morning.I gave a response to mbrooke's point.
A specific, real life example. Whether I said it or not doesn't change that.
Life moves on.I know. You were talking about one thing and Iwire another. Iwire took it to mean you were saying reducing the total load would not subsequently reduce neutral current. Just struck me as funny this morning.
Suppose you have a load which is 99% 3rd harmonic and 34% load on each phase then the neutral is still over 100% loaded.Suppose you have a load which is 75% third harmonic.
Load each phase to only 50%.
Third harmonic per line is then 37.5%.
Total neutral current is then 112%.
Note that neutral current is then over 100% for a full sized neutral and the line current is not "in the upper end".
Sent from my XT1585 using Tapatalk
Wow, i didnt realize reducing a nuetral thread could be so entertaining
Sent from my iPhone using Tapatalk
.What about a large job with hundreds or thousands of feet of large wire?
.
we don't have that here. we are talking the difference between 2/0 and 1/0 aluminum,
in a single service riser. i was generous calling it at 20'. under $3 direct costs.
i do service changes at $2,200. i use copper, and i don't derate
the neutral, and it's about a $1,500 day clear, subtracting
materials and fixed operating costs for the day, and wasting
all that money on copper wire. and i will hit base hits like that
every day they get pitched to me. 4 of them a week, 50 weeks
a year is $300k net taxable, just ripping out cans.
seeing as we are picking flypoop out of pepper, and leaving
my two worthless posts out of the count, we now have a
delta of $2.80, divided by 113 posts. your posts have now
changed from a value of $0.0538 to $0.0247787611.
that's my two cents worth.
Suppose you have a load which is 75% third harmonic.
Load each phase to only 50%.
Third harmonic per line is then 37.5%.
Total neutral current is then 112%.
Note that neutral current is then over 100% for a full sized neutral and the line current is not "in the upper end".
Sent from my XT1585 using Tapatalk
BTW, you know how forum members here created a phase/neutral current Xcel sheet? Can someone do the same factoring harmonics:angel:
Id argue that still holds true outside of the nurse's office.
.
we don't have that here. we are talking the difference between 2/0 and 1/0 aluminum,
in a single service riser. i was generous calling it at 20'. under $3 direct costs.
i do service changes at $2,200. i use copper, and i don't derate
the neutral, and it's about a $1,500 day clear, subtracting
materials and fixed operating costs for the day, and wasting
all that money on copper wire. and i will hit base hits like that
every day they get pitched to me. 4 of them a week, 50 weeks
a year is $300k net taxable, just ripping out cans.
seeing as we are picking flypoop out of pepper, and leaving
my two worthless posts out of the count, we now have a
delta of $2.80, divided by 113 posts. your posts have now
changed from a value of $0.0538 to $0.0247787611.
that's my two cents worth.