I went on a service call to a large custom home that was only a couple of years old. The home was wired with #14 and the runs were quite long. The homeowner worked out of his home and had an office set up on the upper level. The panel was in the basement.
He had a lot of computer equipment, laser printers, etc. His voltage kept dropping low enough that his computers would shut down. He had a power monitor connected to the computers and he could see the voltage dropping.
I can't remember the exact voltage drop but it was something like 12 to 15 percent when I checked it with my voltage drop tester.
I ended up running a dedicated #12 20amp circuit to the room and the voltage drop measured about 5 percent if I remember right. Anyways it solved the problem he was having.
It seems to me on some of these very large homes, like this one, that the #14 guage runs can become quite long and seem to have quite a bit of lighting on them so that when anything with a siginificant load is plugged into an outlet voltage drop can become a problem. His breakers were holding up fine it was his computers that were having problems with the voltage drop.
He may very well have had the same problem even if the wiring was #12 but the larger wire I'm sure would have helped with the voltage drop. I think a lot of it comes down to running #14 to cut costs but also loading up the circuits too much to save money as well. They load up the circuit with can lights and run the receptacles off the same circuit as well.
I can see this as becoming more of a problem when they have to install AFCI breakers for all the circuits. They'll try to skimp on the number of circuits as much as possible to reduce the number of AFCI breakers they install.
Does anyone do voltage drop calculations when running these circuits in overly large homes?
Often times they don't install panels throughout the home but install everything in an equipment room located in the basement. This can lead to some long runs by the time you get up to the upper levels.
He had a lot of computer equipment, laser printers, etc. His voltage kept dropping low enough that his computers would shut down. He had a power monitor connected to the computers and he could see the voltage dropping.
I can't remember the exact voltage drop but it was something like 12 to 15 percent when I checked it with my voltage drop tester.
I ended up running a dedicated #12 20amp circuit to the room and the voltage drop measured about 5 percent if I remember right. Anyways it solved the problem he was having.
It seems to me on some of these very large homes, like this one, that the #14 guage runs can become quite long and seem to have quite a bit of lighting on them so that when anything with a siginificant load is plugged into an outlet voltage drop can become a problem. His breakers were holding up fine it was his computers that were having problems with the voltage drop.
He may very well have had the same problem even if the wiring was #12 but the larger wire I'm sure would have helped with the voltage drop. I think a lot of it comes down to running #14 to cut costs but also loading up the circuits too much to save money as well. They load up the circuit with can lights and run the receptacles off the same circuit as well.
I can see this as becoming more of a problem when they have to install AFCI breakers for all the circuits. They'll try to skimp on the number of circuits as much as possible to reduce the number of AFCI breakers they install.
Does anyone do voltage drop calculations when running these circuits in overly large homes?
Often times they don't install panels throughout the home but install everything in an equipment room located in the basement. This can lead to some long runs by the time you get up to the upper levels.