I am being told that a GFCI is needed under a sink, but I cant find anything in 2014 NEC requiring that. Inspector claims its in there. :blink:
I am being told that a GFCI is needed under a sink, but I cant find anything in 2014 NEC requiring that. Inspector claims its in there. :blink:
210.8(A)(7) states (for dwelling) within 6' of a sink. I suspect under the sink is within 6'
Ask the inspector for a Code reference.
I think you will see variations in how this is interpreted, but I think a majority will use the concept that if a six foot long cord plugged into the receptacle will reach the sink then it needs protected, even if a cabinet door needs to be open to do this. This may even make protection required in an upper cabinet receptacle should such a cord be able to reach the sink.I regret to say that's it But that's 6 feet within a sink, not under.
I think you will see variations in how this is interpreted, but I think a majority will use the concept that if a six foot long cord plugged into the receptacle will reach the sink then it needs protected, even if a cabinet door needs to be open to do this. This may even make protection required in an upper cabinet receptacle should such a cord be able to reach the sink.
That is the problem, NEC did not make their intent all that clear and the reason you will see differences in opinions of how to enforce it. I wouldn't be surprised to see a change in 2017 that does clarify the intent to some degree.But I would think if that was the intent of the NEC then it would explicitly say that. If that was indeed the intent then I would need GFCI protection behind the adjacent wall as well the basement ceiling right below the sink.
IMO 6 foot would be the other edges of the sink rather than underneath.
That is the problem, NEC did not make their intent all that clear and the reason you will see differences in opinions of how to enforce it. I wouldn't be surprised to see a change in 2017 that does clarify the intent to some degree.
Garbage disposal and/or dishwasher possiblyWhat is the outlet for if I might ask?
Which came first? The codebook or the handbook.It's been very helpfully and I think those who write the code should have a handbook to clarify things. Guess not.