flashlight
- NY, NY
- Electrician, semi-retired
Inspector just made us open a meter to put a bonding
jumper between the meter pan and service disco.
His reason ? The meter pan was joined to the service disco with
an offset nipple. Nipple had locknut and MIGB with bonding jumper to enclosure and neutral, both inside disco and inside meter enclosure. Inspector said since offset nipple has shoulders on outside of box, instead of threads and another locknut, it doesn't sufficiently bond the 2 enclosures.
I say they are bonded through the locknuts and MIGBs at either end of nipple that are bonded to enclosures. Boss agrees, but said change it anyway since it's not worth fighting with these guys.
Is inspector correct ?