That - in lies the debate we are having... Just because some members of Mike Holts forum believe in the "one side only interpetation" even Mike Holt himself does not make it so. The code clearly does not say one side only, and it clearly does not say both sides either - but in my own interpetation, and a few others it does imply that both are required. So clearly the code needs clarification.
'shall be
bonded together' (in 250/92(A) ) means to me, all connecting parts are bonded... Not at one end or the other - but both.
And 'electrical continuity' - 'ensured by one of the following methods' means just that -
continuity by those methods - nowhere there in 250.92(B) does it say to one side or the other... ('
One of the following methods' does not mean to one side only to me...)
Nor does the use of the word "SOLE". As the base of this debate of 250.92(B) also stands on this wording - "Standard locknuts or bushings shall not be the
sole means for the bonding required by this section" You can clearly have a bonding bushing or locknut inside of the enclosure, and a standard locknut out side the enclosure, but IMO this does not get you out of bonding the other end of the conduit as a whole... (To provide
continuity by the provided means -
bonding the enclosures
together.)
For that matter the code itself makes as if the grounded conductor is connected in one place only because the meter does not exist....
The current is still there, and it is still objectionable... (250.6) But in many localities alterations to stop this current are not available. i.e I can not have SEC's in other than IMC/RMC, and no acceptable fitting comination can be devised to isolate one end. Which is why I find the contradiction near and dear...
I also can not disconnect either bonding jumper. (in most common cases)