You're going to have to show me soemthing that says specifically only the exceptions noted earlier apply and not the general provision. The only use of the word "tap" in the exceptions isn't enough.
Well here is the two sections in question and I ask you to show me where in the main body of the text a tap is mentioned.
It is clear that the taps are covered in detail in the exceptions but not one word is mentioned in the mandatory rule only in the permissive part of the rule or the exception.
(3) Household Ranges and Cooking Appliances. Branch-circuit conductors supplying household ranges, wall-mounted ovens, counter-mounted cooking units, and other household cooking appliances shall have an ampacity not less than the rating of the branch circuit and not less than the maximum load to be served. For ranges of 8? kW or more rating, the minimum branch-circuit rating shall be 40 amperes.
Exception No. 1:  Conductors tapped from a 50-ampere branch circuit supplying electric ranges, wall-mounted electric ovens, and counter-mounted electric cooking units shall have an ampacity of not less than 20 amperes and shall be sufficient for the load to be served. These tap conductors include any conductors that are a part of the leads supplied with the appliance that are smaller than the branch-circuit conductors. The taps shall not be longer than necessary for servicing the appliance.
Exception No. 2:  The neutral conductor of a 3-wire branch circuit supplying a household electric range, a wall-mounted oven, or a counter-mounted cooking unit shall be permitted to be smaller than the ungrounded conductors where the maximum demand of a range of 8?-kW or more rating has been calculated according to Column C of Table 220.55, but such conductor shall have an ampacity of not less than 70 percent of the branch-circuit rating and shall not be smaller than 10 AWG.
(4) Other Loads. Branch-circuit conductors that supply loads other than those specified in 210.2 and other than cooking appliances as covered in 210.19(A)(3) shall have an ampacity sufficient for the loads served and shall not be smaller than 14 AWG.
Exception No. 1:  Tap conductors shall have an ampacity sufficient for the load served. In addition, they shall have an ampacity of not less than 15 for circuits rated less than 40 amperes and not less than 20 for circuits rated at 40 or 50 amperes and only where these tap conductors supply any of the following loads:
(a)  Individual lampholders or luminaires with taps extending not longer than 450 mm (18 in.) beyond any portion of the lampholder or luminaire.
(b)  A luminaire having tap conductors as provided in 410.117.
(c)  Individual outlets, other than receptacle outlets, with taps not over 450 mm (18 in.) long.
(d)  Infrared lamp industrial heating appliances.
(e)  Nonheating leads of deicing and snow-melting cables and mats.
Exception No. 2:  Fixture wires and flexible cords shall be permitted to be smaller than 14 AWG as permitted by 240.5.