I was referring to other solution methods. Plus, I am using these values:
			Vab = 482.000000000<0.000000000?
Vbc = 479.000000000<-121.000000000?
Vca = 473.226244709<119.816136066?
which convert to:
Va = 278.282829749<-30.000000000?
Vb = 276.550778942<-151.000000000?
Vc = 273.217299771<89.816136066?
I also have resistances of:
Zab = 12.000000000<0.000000000?
Zbc = 8.000000000<0.000000000?
Zca = 4.800000000<0.000000000?
and so have currents of :
Iab = 40.166666667<0.000000000?
Ibc = 59.875000000<-121.000000000?
Ica = 98.588800981<119.816136066?
which produce measured values of:
Ia = 123.576152816<-43.803702128?
Ib = 87.611006252<-144.140179271?
Ic = 138.063536773<97.567541062?
I believe
this is at the heart of the problem.
Line-to-line voltage angles can vary due to line-to-neutral voltage magnitudes and angles departing from nominal (i.e. either or a combination of both).  However, no matter which, the neutral voltage point, be it virtual or real, must be common to all L-N vectors.  If we take your L-L voltages and arrange the vectors head to tail in a triangle, and your L-N vectors heads to the triangle's vertices...
...your L-N vectors tails should coincide at a single neutral point... but they do not.
Even if we extended the two shorter ones (white dashed lines represent extentions in illustration), they don't even meet at a single point.
I believe you are assuming the line voltage source is a wye secondary. There is no way to know whether the L-L voltage angle shift from nominal is a result of voltage or angle deviation, or a combinaiton of both.
Regardless, the delta load will find its own virtual neutral voltage point (since there is no real neutral voltage point).  I am uncertain how it does that at the moment (perhaps for all eternity too :roll
 but I have been assuming it mimics a first fermat point vectorially. Perhaps it may be an incenter.  If your care to try the calculations again for either or both, here's the data...
First Fermat Point vectors
Va=274.9563362159<-30.3946417627
Vb=281.5961211068<-150.3946417626
Vc=271.4745657892<-270.3946417626
Incenter vectors
Va=275.2046453513<-30.0919319670
Vb=280.2151795898<-150.5000000000
Vc=272.6131289725<-270.5919319669
I'd try 'em myself, but my mind is distracted with another "real" project.