Hello everyone!  I am new to the site and have a problem that I need help with.
I have a 120/208v panel that has a shunt trip breaker in it. the purpose of the breaker is to kill the panel in the event of emergency. the breaker itself has three control wires....a black, a red, and a white. the e-stop circuit consists of a 120v circuit that feeds one side of a n/o momentary contact pushbutton. the other side of that contact returns to the black wire on the breaker to trip it open. there is also a momentary contact n/o keyed switch at the e-stop location that has the same feed as the pushbutton. the other side of that contact returns to the red wire on the breaker to ( i assume) close it after the emergency situation is resolved.
I have two problems with this.
#1 I can't make the breaker shunt open when I apply 120v to either the black or red on the breaker...( the white is landed on the neutral bar)
#2 the 120v for the e-stop circuit is fed from the very panel that the shunt trip breaker is intended to de-energize so if i do get the breaker to open the control power will be gone and that will prevent closing the breaker.
I am finishing a job that someone else started and trying to piece this together without knowing what demoed or why
thanks for any help that can be offered