- Illinois
- retired electrician
Why would anyone even think about using 2000 kcmil?Some of you would know better than I
what size conduit for 12 x 2000 mcm?
sounds like a tough pull?
No one would do a 50% ampacity adjustment on a feeder either.they wouldn't
but it is the only size that 'fits' for 4000 A, 50% derated, isophase lol
Thanks for pointing that out. So if you fix the maximum number of CCCs in a conduit (to either 3 or 6 as desired):In my picture there are four current carrying conductors in each conduit which requires an 80% derate.
Had they been installed in the conventional way (A, B, C, N) there would be no need for derating.
For a three phase feeder with a neutral, isophase requires (a bit over) 4/3 as many conduits, because you don't get to take credit for the neutral as a non-CCC.
For a three phase feeder without a neutral, the hit from isophase isn't as severe: just round up the number of conduits to the next multiple of 3.
Cheers, Wayne
I think you are the only one that mentioned that for conduits. I mentioned it for wireway, which is where you may have got the notion mixed.someone also mentioned that conduit must be derated for isophase to 20% fill
I haven't verified that
To make it easier to maintain same length on each conductor of one phase.as far as using isophasing and limiting to 3 conductors, at that point what is the advantage?
terminations would still be as complex as the abc method?
I don't understand this comment--isophase doesn't restrict you to one conduit per phase (see the pretty picture iwire posted). So if you go above 6 CCC per phase, run more conduits. Same as in a mixed phase installation.
Cheers, Wayne
Lol
and a Cat D9 winch to pull
back of napkin 7+ inch
isn't 6" the largest pvc?
edit 12"+ at 40% fill
There is a strong lobby here on this thread that is opposed to isophasing.
then why is it done so infrequently?
how much difference will a few inches delta make over 100' run
That is absoulutly false.
I have not seen one person other than Phil state they where against it.
The fact remains regardless if you are for it or against it the NEC PROHIBITS isophase installations except for a very small number of installations.
The NEC does not prohibit isophase installations. They embrace them
300.3(B) Conductors of the Same Circuit. All conductors of
the same circuit and, where used, the grounded conductor
and all equipment grounding conductors and bonding conductors
shall be contained within the same raceway, auxiliary
gutter, cable tray, cablebus assembly, trench, cable, or
cord, unless otherwise permitted in accordance with
300.3(B)(1) through (B)(4).
(1) Paralleled Installations. Conductors shall be permitted
to be run in parallel in accordance with the provisions of
310.10(H). The requirement to run all circuit conductors
within the same raceway, auxiliary gutter, cable tray, trench,
cable, or cord shall apply separately to each portion of the
paralleled installation, and the equipment grounding conductors
shall comply with the provisions of 250.122. Parallel runs
in cable tray shall comply with the provisions of 392.20(C).
Exception: Conductors installed in nonmetallic raceways
run underground shall be permitted to be arranged as isolated
phase installations. The raceways shall be installed in
close proximity, and the conductors shall comply with the
provisions of 300.20(B).
While most do not agree with me, including the members of CMP3, it is my opinion that 300.3(B)(3) permits the use of isolated phase installations anywhere you want to use them. There is no need for the exception to 300.3(B)(1).That is incorrect.:happyno:
Here is the code section from 2014 NEC
The only NEC permitted isophase installations are described in the exception above.
Therefore isophase installations cannot be used for any circuit above ground or in a metal raceway or cable. The eliminates most applications of isophase.
There is a strong lobby here on this thread that is opposed to isophasing. I consider the derating issue is being over exaggerated by those very same folks to "justify" their position. Let them produce the code abstracts to support their statements.