I agree with Rob. The extra bonding requirements for CSST are not found in the NEC and a proposal to put them in the 2011 NEC was rejected (at least so far). These extra-ordinary bonding requirements are found in the CSST manufacturer's instructions, which are not NEC 110.3(B) instructions, and in NFPA 54. The installation of this bonding should fall to the piping contractor and should be inspected by the plumbing inspector. It has nothing to do with the NEC or the scope of the NEC. If local rules prohibit the plumbing contractor from doing this work, then he would have to higher an electrician, but it all belongs on his inspection tickect, not the electrical contractors.