Even with concrete on top of the conduit you still have to be 24"
Even with concrete on top of the conduit you still have to be 24"
Yes, nothing in 300.5 says anything about it being covered with concrete except for note 5, but you have to have the rocky conditon.
Even with concrete on top of the conduit you still have to be 24"
I do. IMO, if it is a concrete commercial driveway or parking lot then the pvc still must be 24" deep--although I can see that as misleading and 2" of concrete would change things.Maybe I missed something. I don't see table 300.5 that way.
We are talking about table 300.5, right? There are two rows dedicated to concrete cover. One with 2" of concrete, the other with 4" of concrete.
Maybe I missed something. I don't see table 300.5 that way.
I do. IMO, if it is a concrete commercial driveway or parking lot then the pvc still must be 24" deep--although I can see that as misleading and 2" of concrete would change things.
In that case, I would use a pre-fab 45 and torch heat another piece to 8 degrees.What if you need 53 degrees of bend
I have never come across that situation with underground PVC installation. In any case, I'm sure I would have enough room in the ditch to get around a 1 inch object. :happyyes:or need to saddle a 1 inch diameter object?
I am not arguing that. If it is a parking lot, no matter the surface, then 24" is the minimum unless there is a need for note 5.
Note 5 does not apply to commercial driveways. If you encounter solid rock you blast! Columns 1,2,3,4,5 all say 24" min cover
Note 5 does not apply to commercial driveways. If you encounter solid rock you blast! Columns 1,2,3,4,5 all say 24" min cover
I don't see anything in Note 5 about commercial driveways. It says where solid rock prevents compliance with the cover depths specified in this table ....
The table lists all types of installations. There might be a local code, but I don't see anything regarding commercial in that note.
I have a charcoal-filled ammo box that I have "identified" for use bending plastic pipe.
What is 'identified?" I just point and say 'there it is!'
Absent actual damage (charring) of the pipe, there's no violation.
I totally agree ! Note 5 has nothing to do with driveways, roads, highways, alleys,and parking lots. 24" min depth with or without concrete.
I believe you are reading too much into it. Where solid rock prevents compliance with the cover depths specified in this table,
Notice it doesn't say what specific installation it covers or doesn't cover. It states, again, Where solid rock prevents compliance with the cover depths specified in this table...
The problem was I didn't read all of it! I knew this but for some reason I just read over it to quickly! :ashamed1:
This is the way I see it.
The concrete cover only applies when there is rock then "the raceways shall be covered by a minimum of 50 mm (2 in.) of concrete extending down to rock." If there is no solid rock at the bottom of the trench concrete is moot.