Wait, that's a leap . . . the snap switch is part of the Premises Wiring System, but that doesn't mean that it's wiring.So, let's turn back to Premises Wiring (System)'s definition [. . .] Note that I did not highlight "wiring devices". I consider that a two word term to mean "devices". A simple snap switch is included as wiring. . .
Busways are conductors, but the only evidence you cite that they are wiring is the title of Chapter 3. I think that is a stretch and most would consider busways to be conductors that aren't wiring. Likewise for the internal conductors of a snap switch.and, obviously, current travels through the conductors inside a simple snap switch. . . do those snap switch internal conductors look like THHN? No. With busway as a guide, I don't think they have to, to be understood as wiring.
What about the "taken to supply" argument?
BTW, I think you argument works if just 2 words were changed in the NEC definitions: in Premises Wiring System, if "does not include wiring internal" were "does not include conductors internal"; and in Outlet, if "taken to supply" were "taken and supplies". But that's not how the definitions read.
Cheers, Wayne