Looks like they let them go in the pipe that way when pulling.How does one get untangled runs of wire through a pull box like this?
![]()
That's four sets of (4) 500 MCM aluminum feeders. Is there a "trick-of-the-trade" to preventing the wire sets from getting twisted, looped, tangled, and/or birds-nested?
I'm not sure what you mean. To me, the above installation looks pretty "clean": all the wires in each set are fairly tight (almost looks like each set is bundled), with smooth sweeping bends and no loops.Looks like they let them go in the pipe that way when pulling.
I'm not sure what you mean. To me, the above installation looks pretty "clean": all the wires in each set are fairly tight (almost looks like each set is bundled), with smooth sweeping bends and no loops.
In contrast, this is what the same box looks like after a different installer pulled out those wires and pulled in a whole new set of
I didn't think that was possible because the individual pull lines seem to invariably get crossed over each other within the conduit. I've only seen wires pulled into conduit as a complete set.I see what you mean now, in this picture, what should have been is each wire at the end of the pull should have been pulled one at a time, just like when you are finishing off an LB so it's nice and neat and UN crossed.
I didn't think that was possible because the individual pull lines seem to invariably get crossed over each other within the conduit. I've only seen wires pulled into conduit as a complete set.
Am I wrong?
Additional information on the above conduit runs: from the pull box in the photos, it's 160 feet in one direction to the main service gear, and 200 feet in the other direction to the main distribution panel.
He doesn't mean do the entire pull one wire at a time. What he means is to tug on each one, one at a time, after they are all pulled in. That makes them come out even and not all goofy looking.
Additional information on the above conduit runs: from the pull box in the photos, it's 160 feet in one direction to the main service gear, and 200 feet in the other direction to the main distribution panel.
I see. But how does one eliminate loops in the wire (like the wires in the center with the red tape on them)? Just pull them hard enough to change the loop into a spiral twist?
Think of it like this, You feed them in the pipe making sure they do not get crossed up.
When you have all the slack at the box stretch them out and make sure they're not crossed up, now feed them in the pipe on the second half of the pull, when there is 3-5 feet left in the loop, have the guys pull one at a time using radios if you are not within earshot.
Agreed. In fact, I'd say it would be virtually impossible to fix them without pulling them out of at least one side and starting over.I think now that it's done you can't really fix it without a lot of extra effort.
I think that would be tough with 160 - 200 feet of 500's.
couple things. use a swivel when pulling, so you don't spiral them.
if you can fit it in the enclosure, a small greenlee pulling wheel is
the ticket. you can pull in one continuous pull.
if you have to work it in in sections, pull the longest leg first,
stretch out the conductors, and put a turn of tape every arm
length, then **remove*** each tape loop as you pull in the
the other direction. if you tape them up evenly, it'll turn out
nice.
if you don't, it'll look like photo two.
Yes it sure would, but what is a better way?
You need to use a swivel on the head. As the rope is pulled it will twist the wires in the pipe!