I'm up to date
I'm up to date
Following Rick's advice, I went back to square one.
From post #1:
jim dungar said:
...There is a single load resistor, so isn't there a single source current either flowing from 1->2 or from 2->1...
No. It is according to your frame of reference.
It is about relativity. See the relative voltages and currents below:
Arguing any different is like arguing power delivered vs power received. It depends which side of the circuit you are standing on. If you say current is only in the positive direction, you MUST have already picked a reference frame or you could not tell what was going on in the circuit.
From post #4
jim dungar said:
...The point I have tried to make is that what ever method is used to describe the voltages should not require an adjustment in order to describe the currents...
True. The signs are by definition. You haven't started one analysis and then started over with a different analysis when you cross the neutral point.
From post #6
jim dungar said:
...Draw the single loop current and the two sources. All I can see is that in a 2-wire node analysis what goes in to the node must come out the presence or absence of a voltage source doesn't change anything.
If you were standing on the node it would look different. When the electron was coming in, you would have to face one way to see it. When the electron leaves, you would have to face the other way to see it.
From post #14
Rick Christopherson said:
Jim, I was wondering, would it help your discussion to look at Power calculations instead of just current?
You will find that there is power entering and leaving a point, even though the electrons did not make a u-turn. Current entering and leaving is analogous power absorbed or power supplied or to positive and negative.
From post #16
jim dungar said:
...or is it acceptable to have a resistive current "out of phase" with its voltage?...
No. In a correct circuit, it won't be because by definition it is not. See response to #1 above
From post #18:
jim dungar said:
...One of two things must occur when using your voltage definition, either the current flow through source Vbn suddenly changes direction
Assuming you are talking about a correct circuit, that is EXACTLY what happens when you cross the neutral point. Think about flying over the north pole. Heading in, you are flying in the north direction. When you cross the pole, you are headed south.
HERE IT IS CLASS...PAY ATTENTION: you just changed direction without making a u-turn because of the way north and south are DEFINED.
I'll say it another way: Drive over the North Pole with your GPS on your window and see if it indicates that you have changed direction.
From post #25
jghrist said:
With the voltages as defined, there will be no current.
Exactly right. But, I did not catch anyone saying that was a legitimate circuit. If they did, tell me which post so I can review (this may be some of the stuff brought over from another thread).
From post #37:
jim dungar said:
I have been trying to point out the advantages and disadvantages of different presentations...Making an adjustment (i.e. so that the voltages seem correct) can lead to having to make other adjustments later...
If talking about corner vs neutral, other than the simple case where we could use the easier walk-through analysis instead of the more complex loop analysis, I don't see choosing the corner verses the neutral for a reference as having a permanent advantageous or disadvantageous label. I also don't want to have to keep adjusting things, but I don't see how choosing the neutral as reference makes me do that. I can't believe that's what you were saying so:
If you are talking about rattus trying to fix the sign error in the simple circuit, I agree. He should have fixed it before starting out.
Post #43 (mivey): This guy sounds like a genius :grin:
From Post #44
rattus said:
The +/- signs are like the polarity dots on a transformer, Not easy to change, and this seems to be a common misconception. If we did that, the two voltages would be IN phase, and there would be zero volts between them.
No. They were drawn in phase to start with (see post #9). It is not a useful circuit. The correct circuit would be to swap the + and - and leave the 180 degrees as shown.
also
From post #60
winnie said:
(discussing the meaning in the diagram way back in post #9)
...Thus the diagram is not self consistent.
Winnie caught that there was a problem. with the circuit diagram as labeled.
From Post #56
rattus said:
True,
Van = Vnb = 115V @ 0.
You are using different references for the two sources. Use "n" for the common
reference.
Agreed. What if your circuit needed +-1.5 volts and you could not find a negative battery (I'll sell you one for $50)? Tie two 1.5 volt batteries in series and use the midpoint as the reference = +- 1.5 volts (I believe Rick addresses this later and shows a nice battery graphic from another thread).
Post #59 (mivey): This guy sounds like an idiot :grin:
Post #62 (winnie): Loved it
From post #64
For the single resistor circuit you should have gotten:
Vbn = -115@180 = 115@0
Van = 115@0
vab = 0
That's correct. This circuit is not drawn to be a useful circuit. See my response to post #44.
For the complex circuit you should have gotten:
Vbn = -115@0 = 115@180
van = 115@0
vab = 230@0
Again Rick is correct. The polarity and angles are drawn correctly for this circuit.
From post #69
rattus said:
...That is clearly the intent of the originator of that sketch...
But instead of trying to make an incorrect diagram work, you should have fixed the diagram first. We are not going to cut anyone any slack here :grin:
From post #70
Rick Christopherson) The simple diagram was flawed to start with. Trying to re-define it on the fly was a mistake. Rick said: "You, on the other hand, are trying to redefine the battery itself..." If that is what Rattus said in the other thread, he is wrong. The batteries on the left are yummy, the ones on the right are yucky.
From post #79
I believe this contradicts what you have stated previously, so I am reluctant to comment on this until a few other members have a chance to comment as well.
Without reading an entire other thread, it sounds like rattus got mixed up in a sign problem and didn't realize it. From his other statements here it would appear he knew what he INTENDED to say and tried to take a stand on what he THOUGHT he said instead of just fixing the original error.