Fascinating thread Mr MBrooke.
Your test methodology is inspiring ,and brings code history to mind.....
If i'm not mistaken, older code cycles flipped back/forth on branch circuit extensions made from non-egc circuitry via gfci's , perhaps you've stumbled on the underlying rationale?
Some of these past concerns predated art 406, and existed in 210.8 , yet here is the '14>>>
406.4(D)(2)(b) comes to mind>
(b) A non-grounding-type receptacle(s) shall be per-
mitted to be replaced with a ground-fault circuit interrupter-
type of receptacle(s). These receptacles shall be marked
"No Equipment Ground." An equipment grounding con-
ductor shall not be connected from the ground-fault circuit-
interrupter-type receptacle to any outlet supplied from the
ground-fault circuit-interrupter receptacle.
as well as the recent 250.130 (C) (4) change>
(4) An· equipment grounding conductor that is part of an-
other branch circuit that originates from the enclosure
where the branch circuit for the receptacle or branch
circuit originates
Bottom line, we've the
tried true toridial ,dependent on the ECG being married to an MBJ in a TN-C-S earthing system.
My Q is, what if this changes? For instance the recent 250.130(c)(4) change may be interpreted by some as installing a ECG off BX
Would this introduce enough R factor to light up your tester bulb?
Conversely, what if your serving Xformer proximity is such that your entire dwelling is essentially a noodle?
~RJ~