Let's say I run two twenty amp circuits to the laundry room. Circuit one serves recepts. in the laundry room only, except the washer.
If circuit two serves the washer and the alarm on a sewer lift have I violated 210.11 or any other relevant code rule.
I think not, but I want to be sure.
Part of the reason for wanting this arrangement is there is a sink in the laundry room. The homeowner prefers to have the required GFCI protection be a breaker rather than recept.