I hear ya! I?m just shocked I had a post run this long
I hear ya! I?m just shocked I had a post run this long
It tried to stop several times, but you just would not let it die until the consensus swung in your direction.I hear ya! I?m just shocked I had a post run this long
Really!? Anyone else on board with david
I still argue that it does not make any sense to require the extra receptacles, but the Code seems to be doing it.
I still contend that it does not make any sense to require the extra receptacles, NOR does the Code REQUIRE them.
If you had an 8' countertop with a 2' endwall at each side for a total measured wall length of 12', you might believe that the countertop would require at least 3 receptacle outlets (ie, 1 receptacle for every 4' of measured wall space.)
But the attached shows only two outlets meeting the code requirements.
View attachment 9269
Just where in the Code does this drawing appear?
Arguably.It doesn't...but it certainly complies with Code requirements.
The ROP comments clearly refer to a Corner counter where excluding the wall at the depth of the counter "could result in receptacles being spaced 6 ft apart where the counter continues along wall."
View attachment 9268
The full faith and credit, count the end wall, folks will tell you that it does not, because a point near the front edge of the countertop near the end wall is more than 24" from the nearest receptacle measuring along the wall from the nearest point on the wall. Two defining factors of the argument have always been whether or not you can choose the counter edge to which you drop your perpendicular from a point on the counter and whether an "as the crow flies" horizontal distance plays any role.
If this were wall outlets in a room, we would have the explicit Code provision that a receptacle not more than 18" from the wall(s) can be treated as providing a required outlet for one or more wall spaces. In this section, since that is not addressed at all, we do not have that assurance, so your assignment of one of the under-cabinet receptacles as covering the space defined by the end wall, 24" away, is on shaky ground. In fact, there is some question about whether a receptacle on the bottom of a cabinet counts at all.
One on the wall, and one in the countertop are both explicitly mentioned.
The ROP comments were also clearly in response to proposals designed to allow exactly what you believe is currently code. They were rejected.
When I wrote my proposal I was pretty sure I was writing about end walls, and proposing that the CMP clarify that end walls should not be required to be included in the wall space measurement. I suppose I could have been writing about hats, sometimes I lose track of things.
Panel Statement: The panel intends that this space be included in the wall line measurement. Exempting the space could result in receptacles being spaced 6 ft apart where the counter continues along wall.