REDUNDANT GFCI

Status
Not open for further replies.
gfci

gfci

How long of a run between the two GFCI's?

The longer the run the more capacitive leakage you may have causing undesired tripping.

If you want "double protection" that is fine but don't put one of them at the beginning of a long run.

What you call a long run . at what length would capacitive leakage become a problem on #10 uf/wg on a gfci?
 
Sort of. Only thing they really care about is that current that goes out comes back on another monitored conductor, then there is also a signal injected that allows them to instantly trip on a neutral to ground fault even if no load current is otherwise present.
Is this something that changed with the last revision on GFCI standards?

I ask because that definitely didn't used to be the case: That was a classic symptom of a NG fault if the GFCI didnt trip until something was plugged in.
 
Is this something that changed with the last revision on GFCI standards?

I ask because that definitely didn't used to be the case: That was a classic symptom of a NG fault if the GFCI didnt trip until something was plugged in.
This is a feature of second generation receptacle GFCIs. Not sure what the history or current situation is on breaker type GFCIs.
I am pretty sure that the GF protection in AFCIs did not include that feature.
 
Is this something that changed with the last revision on GFCI standards?

I ask because that definitely didn't used to be the case: That was a classic symptom of a NG fault if the GFCI didnt trip until something was plugged in.
They have been that way for at least 25-30 years.
 
I do not believe so, I am fairly certain that has been in the last 10 years.
It is only been in the past 10-12 years that the GFCI could detect a neutral to ground fault without a load.

All of the listed GFCIs being manufactured now are of the "self-testing" type. They automatically test themselves and either lock out the power or give an audible and/or visual indication of the failure.
 
This drawing is no different than the instructions included with the GFCI.

And I think I see where iwire was coming from about commercial kitchens not wanting this- instead wanting to be able physically see the gfci in the kitchen. The gfci being right there next to the equipment ensures compliance and makes it easier to reset instead of going to breaker tucked away in a panel.
 
Last edited by a moderator:
And I think I see where iwire was coming from about commercial kitchens not wanting this- instead wanting to be able physically see the gfci in the kitchen. The gfci being right there next to the equipment ensures compliance and makes it easier to reset instead of going to breaker tucked away in a panel.

Very bad things happen when restaurant workers are in a panel.
They turn of freezers and coolers and don't turn them back on.
There are often many panels and they don't know which one to go to.
They don't know the difference between on, off and tripped so they just start switching everything.
Having the GFCI at point of use eliminates all of those problems and saves time too.
 
It is only been in the past 10-12 years that the GFCI could detect a neutral to ground fault without a load.

All of the listed GFCIs being manufactured now are of the "self-testing" type. They automatically test themselves and either lock out the power or give an audible and/or visual indication of the failure.

Neutral to ground faults have tripped GFCI's as long as I can remember. I believe the electronics in older versions (not sure about the new "smart" versions)are connected to the load side so it provides enough load to trigger the ~6ms trip threshold.
 
Curt, that was always true when there was a load on the circuit.

Now they trip load or no load

Bob, old GFCI's would trip without any additional load on the circuit. For as long as I remember I have been able to trip a GFCI by touching the load neutral to ground.
 
Bob, old GFCI's would trip without any additional load on the circuit. For as long as I remember I have been able to trip a GFCI by touching the load neutral to ground.
I never saw that until they changed UL 943 to require neutral ground fault protection.
 
Bob, old GFCI's would trip without any additional load on the circuit. For as long as I remember I have been able to trip a GFCI by touching the load neutral to ground.

I have been in the trade since the early 80s and it has only been fairly recently I have found them to instantly trip.
 