IMO, 110.11 and 110.3(A) will apply only if the NM is permanently installed in a wet location.
So I can leave breakers out in the rain as long as I don't install them there?
IMO, 110.11 and 110.3(A) will apply only if the NM is permanently installed in a wet location.
Per 110.11, he is doing his job. Per common sense, he is asking for a fragging.
So I can leave breakers out in the rain as long as I don't install them there?
We are not talking about breakers. Breakers have moving parts and when left in the rain water will get in and probably cause trouble later on. But NM cable will not leak or even cause trouble when subject to minor wetness.
I am just saying the inspector does not have a leg to stand on.
I don't agree with the 110.3(A)(1) citation, as per the definition of Dry Location "A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction."
OK, then what is the 110.3(A) violation in the OP's situation?There is nothing in 110.3(A) about a dry or wet location.
I agree with you.I agree with you as well
Now show me in the NEC the rule that prohibits breakers out in the rain but allows NM to be out in the rain.
Breaker in wet location is a common sense and I won't find it in the code book, but I will find that NM cable is temporarily allowed in a wet location.
The inspector has the same tools to prohibit NM from being in the rain as breakers, GFCIs etc.
If it is deemed damaged is it still suitable for use?OK, then what is the 110.3(A) violation in the OP's situation?
I thought the idea was that the NM is for dry location only, the rain somehow meant it wasn't a dry location (which is wrong), and that was a 110.3(A)(1) violation.
BTW, do you think that the OP could megger the installed NM to show that it wasn't damaged by the rain, and hence there was no 110.11 violation? Or if the AHJ says it was damaged, there's basically no way to rebut that?
Cheers, Wayne
I don't know, the 110.3(A)(1) language includes the phrase "conformity with the provisions of this Code". If something isn't conforming with another part of the Code, just cite that part directly. The rest of the language in 110.3(A)(1) strikes me at first glance as too vague to be enforceable.I'm not stating whether the cable is actually damaged or not, but if inspector claims it is then isn't 110.3(A)(1) a valid cite from inspectors point of view?
I don't agree with the 110.3(A)(1) citation, as per the definition of Dry Location "A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction."
2011 NEC 110.11, however, says in part "Equipment not identified for outdoor use and equipment identified only for indoor use, such as “dry locations,” “indoor use only,” “damp locations,” or enclosure Types 1, 2, 5, 12, 12K, and/or 13, shall be protected against damage from the weather during construction." So that makes it an AHJ judgement call whether the wind-blown rain has "damaged" the NM cable. Personally that idea sounds crazy, but if that is the AHJ's judgement, is there any way to demonstrate the NM cable is undamaged?
Cheers, Wayne
Equipment. A general term, including fittings, devices, appliances,
luminaires, apparatus, machinery, and the like used as a
part of, or in connection with, an electrical installation.
Nice. Conductors are not equipment as you note. This idea is reinforced by the fact that the first paragraph of 110.11 uses the phrase "conductors or equipment" while the second paragraph of 110.11 just uses the word equipment. So this implies that it is not necessary to protect conductors "against damage from the weather during construction."is NM cable considered "equipment"? does not seem like it from the definition.
If same NM cable has sheath all sliced up, burned off, or full of holes, tears, etc. what is an inspector's basis for not accepting it's use in the installation? If he is to cite a NEC article I'd say 110.3(A) is one possible place to start.I don't know, the 110.3(A)(1) language includes the phrase "conformity with the provisions of this Code". If something isn't conforming with another part of the Code, just cite that part directly. The rest of the language in 110.3(A)(1) strikes me at first glance as too vague to be enforceable.
Cheers, Wayne
OK, then what is the 110.3(A) violation in the OP's situation?
I thought the idea was that the NM is for dry location only, the rain somehow meant it wasn't a dry location (which is wrong), and that was a 110.3(A)(1) violation.
BTW, do you think that the OP could megger the installed NM to show that it wasn't damaged by the rain, and hence there was no 110.11 violation? Or if the AHJ says it was damaged, there's basically no way to rebut that?
is NM cable considered "equipment"? does not seem like it from the definition.
Nice. Conductors are not equipment as you note. This idea is reinforced by the fact that the first paragraph of 110.11 uses the phrase "conductors or equipment" while the second paragraph of 110.11 just uses the word equipment. So this implies that it is not necessary to protect conductors "against damage from the weather during construction."
That leaves us with 0 code violations for NM that gets rained on during construction.
I agree. 110.3 doesn't apply to conductors at all, only equipment.That is an interesting observation and really puts things in disarray as that means 110.3(B) does not apply to any conductors at all.
Well, the NEC is a permissive code. So permission is not required; rather a prohibition on letting NM cable get rained on needs to be demonstrated.Despite the allowance in the definition of dry location there is no permission to let the cable get wet in the NEC or the listing.
A more representative shortening of that rule is 'no conductors shall be located where exposed to liquids that have a deteriorating effect'. So I would say that rain on an intact NM cable sheath does not constitute 'exposure to liquids that have a deteriorating effect'. The water will run off the sheath and not deteriorate anything, which is what we all know.In my opinion I only need the first paragraph of 110.11(A) 'conductors will be protected from liquids'
I agree. 110.3 doesn't apply to conductors at all, only equipment.
In many places the NEC uses the phrase "equipment or conductors" or "equipment or materials"; in others it just says "equipment". So I believe this is an intentional distinction.
Well, the NEC is a permissive code. So permission is not required; rather a prohibition on letting NM cable get rained on needs to be demonstrated.
A more representative shortening of that rule is 'no conductors shall be located where exposed to liquids that have a deteriorating effect'. So I would say that rain on an intact NM cable sheath does not constitute 'exposure to liquids that have a deteriorating effect'. The water will run off the sheath and not deteriorate anything, which is what we all know.
Anyway, that's how I see it.