422.16(B)(4) Range Hoods. Range hoods shall be permitted to be
cord-and-plug-connected with a flexible cord identified as
suitable for use on range hoods in the installation instruc-
tions of the appliance manufacturer, where all of the fol-
lowing conditions are met:
(1) The flexible cord is terminated with a grounding-type
attachment plug.
Exception: A listed range hood distinctly marked to iden-
tify it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.
(2) The length of the cord is not less than 450 mm (18 in.)
and not over 900 mm (36 in.).
(3) Receptacles are located to avoid physical damage to the
flexible cord.
(4) The receptacle is accessible.
(5) The receptacle is supplied by an individual branch
circuit.
It does not matter what the draw is as the code is definitive on this rule. One could also ask the same about an under cabinet light on a SABC. It is just not allowed and it is easier to write the code as it is rather than to make all kinds of allowances.A kitchen hood fan cannot be fed off of the small appliance circuit. How much does a hood fan typically draw?
Feedback appreciated
Fed off of SABCs here all the time.
Um, are you not an inspector?
Take note of number (5) if it's cord and plug connected.
I should have answered NO but did not want to complicate things.![]()
So what's the story with hoods being fed off of SABC's? I guess that was my question....
Same way you would supply power to a micro.
You cant use the SABC to supply power to a fixed microwave either... what am i missing?
And that is different from a appliance garage outlet how?
I dont understand? A receptacle that supplies the countertop is ALLOWED on the SABC... A fixed microwave or hood is not... Not sure what the confusion is?
(5) Receptacle Outlet Location. Receptacle outlets shall
be located on or above, but not more than 500 mm (20 in.)
above, the countertop. Receptacle outlet assemblies listed
for the application shall be permitted to be installed in
countertops. Receptacle outlets rendered not readily accessible
by appliances fastened in place, appliance garages,
sinks, or rangetops as covered in 210.52(C)(1), Exception,
or appliances occupying dedicated space shall not be considered
as these required outlets.
I can mount a receptacle more than 20" above the counter - it just doesn't count as required.
You're confusing... The OP's topic was a hood not being on a SABC, you stated that its done all the time, my question was why it was allowed.
The OP is wrong.
It is done all the time because it is not prohibited.
What do you call the microwave circuit? Lighting? Laundry? Outdoor?
I would call it a branch circuit, but it cannot be a SABC that is required in the NEC.... This is pretty clear in the NEC. You pick a lot of battles and I think you lose everyone...
Simply read 210.52 (B) (2)
(3) Kitchen Receptacle Requirements. Receptacles installed
in a kitchen to serve countertop surfaces shall be
supplied by not fewer than two small-appliance branch circuits,
either or both of which shall also be permitted to supply
receptacle outlets in the same kitchen and in other rooms
specified in 210.52(B)(1). Additional small-appliance branch
circuits shall be permitted to supply receptacle outlets in the
kitchen and other rooms specified in 210.52(B)(1). No smallappliance
branch circuit shall serve more than one kitchen.
Whats that mean?