Has repeatedly been mentioned the disconnecting means (the one required within 30 feet of the "trailer") must be suitable for use as service equipment - even if not installed as a "service disconnecting means".
How many items can you find that are "suitable for use as service equipment" that don't either contain overcurrent protective devices or at very least require additional overcurrent protection devices. When the device is a non fused safety switch - that would require additional overcurrent protection - most of those I have seen (especially if used on service conductors, though in this case are used on a feeder) require fuses as the protection. Can we disregard the fuse requirement here since this is a feeder as long as the available fault current doesn't present an issue with the switch rating? Many non fused safety switches are only rated 10kAIC unless protected with fuses. That said I bet the available fault current at OP's disconnect location is less then 10kA anyway.
You do not get the point.
OP kept wanting fuses in the beginning to protect feeder.....
Then was throwing in that 80 feet matters for the breaker to work....
Then at some point to protect interior panel, but since it is a trailer inside panel needs its own breaker....
The whole thread would have been different if we had started with 550.32(A), but we did not...