Jim W in Tampa
Senior Member
- Location
- Tampa Florida
210.11(C)(2) says receptacle outlet(s) required by 210.52(F).
210.52(F) only requires 1 receptacle outlet.
What 210.11(C)(2) permits is more than 1 receptacle outlet to be installed on the required laundry branch circuit, but it does not require that all receptacles installed in the laundry area to be installed on that required circuit.
Chris
I agree with most of that.
Now tell me how a receptacle that is in the laundry room is not a laundry receptacle ?